I have a Friday question for the forum, and maybe Roland is able to
respond with some "intent" perspective. In a 27' high industrial  spec
building, we installed sprinkler heads rated at 286 degree. This was
permitted, installed, inspected and approved. The owner now has a tenant
lease which will build out the entire building as a retail furniture
showroom, no ceiling and no storage. The local fire inspector is siting
NFPA 2002 Edition section 8.3.2.2,  "Where maximum ceiling temperatures
exceed 100 degrees F, sprinklers with temperature ratings in accordance
with  the maximum ceiling temperatures of Table 6.2.5.1 shall be used."
, as a requirement to remove all the sprinklers in the building and
replace them with 212 degree F sprinklers.  My contention is that the
next section,  8.3.2.3 "High temperature sprinklers shall be permitted
to be used throughout ordinary and extra hazard occupancies and as
allowed in this standard and other NFPA codes and standards.", allows
the ex  isting 286 degree sprinklers to remain and be in compliance with
NFPA 13. What say the professionals, Roland, Steve, George, Ron, Rod,
Anyone .....?
Mark at Aero
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to