Let's just say that I value the very broad base of experience you have amassed 
in working in the California market.   :-)
Mark at Aero

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton
Sent: Friday, September 28, 2012 10:30 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement

Just to clarify - are you lumping me into the set of "professionals", or hoping 
that I know of one who can speak to this issue?

SL 




-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of 
mphe...@aerofire.com
Sent: Friday, September 28, 2012 10:00 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement

I have a Friday question for the forum, and maybe Roland is able to respond 
with some "intent" perspective. In a 27' high industrial  spec building, we 
installed sprinkler heads rated at 286 degree. This was permitted, installed, 
inspected and approved. The owner now has a tenant lease which will build out 
the entire building as a retail furniture showroom, no ceiling and no storage. 
The local fire inspector is siting NFPA 2002 Edition section 8.3.2.2,  "Where 
maximum ceiling temperatures exceed 100 degrees F, sprinklers with temperature 
ratings in accordance with  the maximum ceiling temperatures of Table 6.2.5.1 
shall be used."
, as a requirement to remove all the sprinklers in the building and replace 
them with 212 degree F sprinklers.  My contention is that the next section,  
8.3.2.3 "High temperature sprinklers shall be permitted to be used throughout 
ordinary and extra hazard occupancies and as allowed in this standard and other 
NFPA codes and standards.", allows the ex  isting 286 degree sprinklers to 
remain and be in compliance with NFPA 13. What say the professionals, Roland, 
Steve, George, Ron, Rod, Anyone .....?
Mark at Aero
 

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to