>From a heat release aspect, and having had a somewhat recent furniture store fire nearby, I think you'll get hot enough fast enough to start popping heads very quickly. In fact I'd think that the 286 heads would be better at keeping the rings not really covering the fire from going off too soon. Not based on data mind you, just me thinking, and that's a dangerous course to steer by.
On Fri, Sep 28, 2012 at 10:47 AM, Steve Leyton <[email protected]>wrote: > Snake oil sales talk at its finest. I believe that part of the > reasoning behind section 8.3.23 (new to the 2010 ed., BTW) was for > applications such as this. I agree with you that replacement of the > sprinklers is not required. Is the AHJ working from the 2010 edition or > an earlier one - could that be the issue? > > Steve > > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of > [email protected] > Sent: Friday, September 28, 2012 10:39 AM > To: [email protected] > Subject: RE: Sprinkler head Temperature requirement > > Let's just say that I value the very broad base of experience you have > amassed in working in the California market. :-) > Mark at Aero > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Steve > Leyton > Sent: Friday, September 28, 2012 10:30 AM > To: [email protected] > Subject: RE: Sprinkler head Temperature requirement > > Just to clarify - are you lumping me into the set of "professionals", or > hoping that I know of one who can speak to this issue? > > SL > > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of > [email protected] > Sent: Friday, September 28, 2012 10:00 AM > To: [email protected] > Subject: RE: Sprinkler head Temperature requirement > > I have a Friday question for the forum, and maybe Roland is able to > respond with some "intent" perspective. In a 27' high industrial spec > building, we installed sprinkler heads rated at 286 degree. This was > permitted, installed, inspected and approved. The owner now has a tenant > lease which will build out the entire building as a retail furniture > showroom, no ceiling and no storage. The local fire inspector is siting > NFPA 2002 Edition section 8.3.2.2, "Where maximum ceiling temperatures > exceed 100 degrees F, sprinklers with temperature ratings in accordance > with the maximum ceiling temperatures of Table 6.2.5.1 shall be used." > , as a requirement to remove all the sprinklers in the building and > replace them with 212 degree F sprinklers. My contention is that the > next section, 8.3.2.3 "High temperature sprinklers shall be permitted > to be used throughout ordinary and extra hazard occupancies and as > allowed in this standard and other NFPA codes and standards.", allows > the ex isting 286 degree sprinklers to remain and be in compliance with > NFPA 13. What say the professionals, Roland, Steve, George, Ron, Rod, > Anyone .....? > Mark at Aero > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120928/b1150e2c/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum