as Todd already said, it is explicitly allowed by 8.3.2.3 unless the AHJ is trying to call it a light hazard occupancy.

Roland

On Sep 28, 2012, at 10:00 AM, <mphe...@aerofire.com> <mphe...@aerofire.com > wrote:

I have a Friday question for the forum, and maybe Roland is able to respond with some "intent" perspective. In a 27' high industrial spec building, we installed sprinkler heads rated at 286 degree. This was permitted, installed, inspected and approved. The owner now has a tenant lease which will build out the entire building as a retail furniture showroom, no ceiling and no storage. The local fire inspector is siting NFPA 2002 Edition section 8.3.2.2, "Where maximum ceiling temperatures exceed 100 degrees F, sprinklers with temperature ratings in accordance with the maximum ceiling temperatures of Table 6.2.5.1 shall be used." , as a requirement to remove all the sprinklers in the building and replace them with 212 degree F sprinklers. My contention is that the next section, 8.3.2.3 "High temperature sprinklers shall be permitted to be used throughout ordinary and extra hazard occupancies and as allowed in this standard and other NFPA codes and standards.", allows the existing 286 degree sprinklers to remain and be in compliance with NFPA 13. What say the professionals, Roland, Steve, George, Ron, Rod, Anyone .....?