All good points.  Gayle, your question was about one specific aspect of an 
inspection per NFPA 25, to which I offered a specific answer.  As Ron alludes 
to, there are numerous other aspects to NFPA 25 conformance regarding a dry 
system.   I wouldn't want anyone basing their defense in a claim or a tort on 
whether or not a visual inspection from the floor meets the overall standard of 
care as prescribed by NFPA 25.
 
SL

________________________________

From: [email protected] on behalf of Ron Greenman
Sent: Fri 11/9/2012 4:00 PM
To: [email protected]
Subject: Re: NFPA 25



But if he does the tests and/or maintenance as well he's supposed to drain
the lowpoints, even if in the attic. We have a contractor in a lawsuit over
the same thing where the installing contractor did nothing to indicate
location and then the sheetrocker hid several in the walls and the
insulator covered another bunch.

On Fri, Nov 9, 2012 at 2:26 PM, GAYLE KNOWLES <[email protected]> wrote:

>
> Thanks Steve.  The reason I ask this is because we have a contractor here
> who is in a lawsuit because the attic system froze up in a building that he
> inspects.  They are blaming him because he does their inspections and
> should've checked the attic system.  We are trying to help him out with as
> much  feedback from our peers as we can get.  AFSA sent us an informal
> interpretation which helps.
>
> Gayle Knowles, SET,RME
> Project Manager
> Kaufman Fire Protection
> 505-884-2447 x207
>
>
>
> > Subject: RE: NFPA 25
> > Date: Tue, 6 Nov 2012 08:50:34 -0800
> > From: [email protected]
> > To: [email protected]; [email protected]
> >
> > That's correct.
> >
> > ________________________________
> >
> > From: [email protected] on behalf of GAYLE
> KNOWLES
> > Sent: Tue 11/6/2012 7:26 AM
> > To: sprinklerforum
> > Subject: NFPA 25
> >
> >
> >
> >
> > According to NFPA 25, one is to observe from the floor when inspecting a
> system. Would this mean that you are not required to crawl around in an
> attic to check for proper pitch and drainage on a dry system?
> >
> > Gayle Knowles, SET,RME
> > Project Manager
> > Kaufman Fire Protection
> > 505-884-2447 x207
> >
> > -------------- next part --------------
> > An HTML attachment was scrubbed...
> > URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121106/96049be4/attachment.html
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >
> > -------------- next part --------------
> > An HTML attachment was scrubbed...
> > URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121106/3465383c/attachment.html
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121109/314a7644/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121109/38f9ac31/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121109/04e7c43a/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to