I'm aware of the dynamics and how the process is going in the current cycle.  I 
teach NFPA 25 for NFPA.   But "blood on their hands" is a bit much, no?  I was 
looking for Dick Patton's name in the signature line.  I am out of country and 
not able to access information I have in my office, but I believe that more 
than 65% of all sprinkler failures are related to water supply encumbrances, 
mostly incorrectly closed valves.   Design deficiencies or changes of use 
without corresponding upgrades to sprinkler system are the next most common 
cause, catgegorically.   BOTH of which are easily correctable by statutory 
conformance with applicable building/fire codes and NFPA 25.   Installation 
deficiencies are important, and I agree with the overall sentiment that it's in 
our industry's very best interest to raise the standard of care as high as 
possible both during and after installation, but that cause of failure isn't 
even on the list, if I recall correctly.
 
SML
 
 

________________________________

From: [email protected] on behalf of Jim Davidson
Sent: Mon 11/12/2012 2:35 PM
To: [email protected]
Subject: RE: NFPA 25



Steve,

What some are trying to do is to make the inspecting contractor responsible for 
the items missed by the Owner's design team engineers and the AHJ reviewing the 
original sprinkler system shop drawing. If every one reads NFPA 25 2008 
paragraph 1.1.2  "The types of systems addressed by this standard include, but 
are not limited to, sprinkler, standpipe and hose, fixed water spray, and foam 
water. Included are the water supplies that are part of these systems, such as 
private fire service mains and appurtenances, fire pumps and water storage 
tanks, and valves that control system flow. The document also addresses 
impairment handling and reporting. This standard applies to fire protection 
systems that have been properly installed in accordance with generally accepted 
practices. Where a system has not been installed in accordance with generally 
accepted practices, the corrective action is beyond the scope of this standard. 
The corrective action to ensure that the system performs in a satisfactory 
manner shall be in accordance with the appropriate installation standard." This 
clearly defines that incorrectly installed systems are not part of this 
standard, the inspecting contractor should notify the Building Owner of the 
original system deficiencies found in a separate letter to the Owner and not as 
part of the NFPA 25 inspection report.

This is just my opinion.

Regards

Jim 




DAVIDSON ASSOCIATES

Fire Protection Engineering     P. O. Box 4010
Code Consultants        Greenville, DE  19807-0010
Medical Gas Systems Engineering (302) 994-9500
        Fax (302) 234-1781


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Monday, November 12, 2012 4:16 PM
To: [email protected]
Subject: RE: NFPA 25

I have read and re-read this three times.  As respectfully and tactfully as I 
can phrase it, what the hell are you talking about?

SML


________________________________

From: [email protected] on behalf of å... ....
Sent: Mon 11/12/2012 9:14 AM
To: [email protected]
Subject: NFPA 25



To date, NFPA 25 has more blood on its hands than the Red Cross.  It 
purposefully avoids tackling improvements to sprinkler inspections,  and that 
injures fire protection's most reliable, cost-effective, and greenest tool.  
Solving the money liability issues has proved complicated, but customers and 
society deserve the effort.

scot deal
excelsior fire
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121112/c181b243/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


-------------- next part --------------
A non-text attachment was scrubbed...
Name: winmail.dat
Type: application/ms-tnef
Size: 4400 bytes
Desc: not available
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121112/3db40d79/attachment.bin>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


-------------- next part --------------
A non-text attachment was scrubbed...
Name: winmail.dat
Type: application/ms-tnef
Size: 7388 bytes
Desc: not available
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121112/a9b96a2a/attachment.bin>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to