Chris, the way I read 23.4.4.1.1.4 is that it's optional.  In your case, I'd
calc 2,000 sf of dry system plus 1,900 sf of wet.  Since it's all light
hazard, it shouldn't get ugly.

I gotta believe there will be some tweaking to that section, though.  I read
the ROP and ROC - Tracey's 480 sf canopy (page 88 of the ROC) is probably
being protected by 4 sprinklers, but could require a 4" supply pipe & dry
valve since the phantom flow is added at the end of the dry x-main.  That
doesn't seem reasonable to me.

Ed Kramer
Lawrence, KS



> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum-
> [email protected]] On Behalf Of Cahill, Christopher
> Sent: Wednesday, March 13, 2013 4:46 PM
> To: [email protected]
> Subject: Phantom Flow
> 
> Not what you think by the subject.  Working out of NFPA 13 '13
> 23.4.4.1.1.5.  This is new and confusing us greatly.
> 
> I have a 20,000 sq.ft. heated LH building. And a 2,000 sq.ft. area that
> needs a dry system.  Not an auxiliary dry system.  My starting required
> design is  0.1/3,900.  I calc the system at 2,000 sq.ft. (cuz that's all
> I have) and get for discussion sake 220 gpm.  Then I subtract from 390
> (3,900 x 0.1 per 23.4.4.1.1.5) and I get 170 gpm.  Then I go back to the
> calc and redo but this time I add 170 at the end of the main.  Now this
> has the effect of overflowing all the rest of the BL's such my final
> calc is more than 390.
> 
> !@#$^#
> 
> What if I have a 500 sq.ft. building and the next building is 20 miles
> away  @#$@# are we calc'ing this extra area for?
> 
> Can someone 'splain if we got it right and then why in the world this
> got into the standard?
> 
> Chris Cahill, PE*
> Senior Fire Protection Engineer, Aviation & Facilities Group Burns &
> McDonnell
> 8201 Norman Center Drive
> Bloomington, MN 55437
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]<mailto:[email protected]>
> www.burnsmcd.com<http://www.burnsmcd.com/>
> 
> Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered
> in: MN
> 
> 
> 
> 
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
> ments/20130313/26a3e378/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to