Military UFC so can't resort to room design method. 

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Mark A. Sornsin, 
P.E.
Sent: Thursday, March 14, 2013 11:13 AM
To: [email protected]
Subject: RE: Phantom Flow

This strikes me as overthinking run amok.  I'm surprised it made it through to 
the final document. Is the logic that the area/density method requires flowing 
over the entire area? Thus, if your area is smaller than the required area you 
have a choice: use room design method, or add this phantom flow.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Cahill, 
Christopher
Sent: Wednesday, March 13, 2013 4:46 PM
To: [email protected]
Subject: Phantom Flow

Not what you think by the subject.  Working out of NFPA 13 '13 23.4.4.1.1.5.  
This is new and confusing us greatly.

I have a 20,000 sq.ft. heated LH building. And a 2,000 sq.ft. area that needs a 
dry system.  Not an auxiliary dry system.  My starting required design is  
0.1/3,900.  I calc the system at 2,000 sq.ft. (cuz that's all I have) and get 
for discussion sake 220 gpm.  Then I subtract from 390 (3,900 x 0.1 per 
23.4.4.1.1.5) and I get 170 gpm.  Then I go back to the calc and redo but this 
time I add 170 at the end of the main.  Now this has the effect of overflowing 
all the rest of the BL's such my final calc is more than 390.

!@#$^#

What if I have a 500 sq.ft. building and the next building is 20 miles away  
@#$@# are we calc'ing this extra area for?

Can someone 'splain if we got it right and then why in the world this got into 
the standard?

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]<mailto:[email protected]>
www.burnsmcd.com<http://www.burnsmcd.com/>

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: MN 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to