I'd argue you are OK because you are not using density/area method. Section 
always talks about area.  You have no minimum area.

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, March 14, 2013 9:58 AM
To: [email protected]; [email protected]
Subject: RE: Phantom Flow

Wow. We are doing a project with a canopy that I don't think needs to be 
sprinkler but that isn't the point. The canopy is 3'-11" wide, sloped greater 
than 2 in 12, requires a dry system and is 600' long. Section 11.2.3.4.2 
requires 7 heads maximum. Would 23.4.4.1.1.4 apply and if so how would it be 
applied? The minimum design area would be 0.20 gpm over 2,535 sqft. The canopy 
is 2,400 sqft and only has one branch line with 48 sprinklers.

Ron F

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ed Kramer
Sent: Wednesday, March 13, 2013 6:51 PM
To: [email protected]
Subject: RE: Phantom Flow

Chris, the way I read 23.4.4.1.1.4 is that it's optional.  In your case, I'd 
calc 2,000 sf of dry system plus 1,900 sf of wet.  Since it's all light hazard, 
it shouldn't get ugly.

I gotta believe there will be some tweaking to that section, though.  I read 
the ROP and ROC - Tracey's 480 sf canopy (page 88 of the ROC) is probably being 
protected by 4 sprinklers, but could require a 4" supply pipe & dry valve since 
the phantom flow is added at the end of the dry x-main.  That doesn't seem 
reasonable to me.

Ed Kramer
Lawrence, KS



> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum- 
> [email protected]] On Behalf Of Cahill, Christopher
> Sent: Wednesday, March 13, 2013 4:46 PM
> To: [email protected]
> Subject: Phantom Flow
> 
> Not what you think by the subject.  Working out of NFPA 13 '13 
> 23.4.4.1.1.5.  This is new and confusing us greatly.
> 
> I have a 20,000 sq.ft. heated LH building. And a 2,000 sq.ft. area 
> that needs a dry system.  Not an auxiliary dry system.  My starting 
> required design is  0.1/3,900.  I calc the system at 2,000 sq.ft. (cuz 
> that's all I have) and get for discussion sake 220 gpm.  Then I 
> subtract from 390
> (3,900 x 0.1 per 23.4.4.1.1.5) and I get 170 gpm.  Then I go back to 
> the calc and redo but this time I add 170 at the end of the main.  Now 
> this has the effect of overflowing all the rest of the BL's such my 
> final calc is more than 390.
> 
> !@#$^#
> 
> What if I have a 500 sq.ft. building and the next building is 20 miles 
> away  @#$@# are we calc'ing this extra area for?
> 
> Can someone 'splain if we got it right and then why in the world this 
> got into the standard?
> 
> Chris Cahill, PE*
> Senior Fire Protection Engineer, Aviation & Facilities Group Burns & 
> McDonnell
> 8201 Norman Center Drive
> Bloomington, MN 55437
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]<mailto:[email protected]>
> www.burnsmcd.com<http://www.burnsmcd.com/>
> 
> Proud to be one of FORTUNE's 100 Best Companies to Work For 
> *Registered
> in: MN
> 
> 
> 
> 
> -------------- next part -------------- An HTML attachment was 
> scrubbed...
> URL:
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
> ch ments/20130313/26a3e378/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to