Don't assume that because you have a wood framed building that you must 
sprinkler the attic. Check with the engineer of record to see if this system is 
supposed to be a 13 or 13R. Secondly you can't run over an ordinary hazard room 
in a light hazard occupancy with cpvc unless the room is 400 ft or less. And 
lastly CPVC is not listed for a dry system and you can definitely not use it. A 
read of the blazemaster install and specification manual is highly recommended. 

Rod at Rapid

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brian 
Harris
Sent: Wednesday, July 17, 2013 7:43 AM
To: [email protected]
Subject: CPVC Applications

I'm doing a daycare facility and was leaning towards using BlazeMaster CPVC but 
have a quick question. I know that it is listed and approved for light hazard 
areas which is 90% of the project, what do you do for the other 10%? Do I need 
to run steel for the Kitchen, Janitor's Closet, and small Storage closet? Also, 
since this is a wood framed building I need to sprinkle the Attic but since it 
cannot be used for storage it is light hazard as well, any reason I can't use 
CPVC for the dry system as well?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to