Brian, Don't assume that because you have a wood framed building that you must sprinkler the attic. Check with the engineer of record to see if this system is supposed to be a 13 or 13R. Secondly you can't run over an ordinary hazard room in a light hazard occupancy with cpvc unless the room is 400 ft or less. And lastly CPVC is not listed for a dry system and you can definitely not use it. A read of the blazemaster install and specification manual is highly recommended.
Rod at Rapid -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Brian Harris Sent: Wednesday, July 17, 2013 7:43 AM To: [email protected] Subject: CPVC Applications I'm doing a daycare facility and was leaning towards using BlazeMaster CPVC but have a quick question. I know that it is listed and approved for light hazard areas which is 90% of the project, what do you do for the other 10%? Do I need to run steel for the Kitchen, Janitor's Closet, and small Storage closet? Also, since this is a wood framed building I need to sprinkle the Attic but since it cannot be used for storage it is light hazard as well, any reason I can't use CPVC for the dry system as well? Brian Harris, CET BVS Systems Inc. Sprinkler Division bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org