I think Tyco has a CPVC listed for use in dry systems?

Sent from my iPhone

On Jul 17, 2013, at 9:52 AM, Rod DiBona <[email protected]> wrote:

> Brian,
> 
> Don't assume that because you have a wood framed building that you must 
> sprinkler the attic. Check with the engineer of record to see if this system 
> is supposed to be a 13 or 13R. Secondly you can't run over an ordinary hazard 
> room in a light hazard occupancy with cpvc unless the room is 400 ft or less. 
> And lastly CPVC is not listed for a dry system and you can definitely not use 
> it. A read of the blazemaster install and specification manual is highly 
> recommended. 
> 
> Rod at Rapid
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Brian 
> Harris
> Sent: Wednesday, July 17, 2013 7:43 AM
> To: [email protected]
> Subject: CPVC Applications
> 
> I'm doing a daycare facility and was leaning towards using BlazeMaster CPVC 
> but have a quick question. I know that it is listed and approved for light 
> hazard areas which is 90% of the project, what do you do for the other 10%? 
> Do I need to run steel for the Kitchen, Janitor's Closet, and small Storage 
> closet? Also, since this is a wood framed building I need to sprinkle the 
> Attic but since it cannot be used for storage it is light hazard as well, any 
> reason I can't use CPVC for the dry system as well?
> 
> Brian Harris, CET
> BVS Systems Inc.
> Sprinkler Division
> bvssystemsinc.com<http://bvssystemsinc.com/>
> Phone: 704.896.9989
> Fax: 704.896.1935
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to