A nice low differential dry pipe valve combined with a nitrogen generator is
the way to go.  All sch40 black.
What would George say?
TD

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rod
DiBona
Sent: Wednesday, July 17, 2013 11:36 AM
To: [email protected]
Subject: RE: CPVC Applications

Ahhh.. yes..... good catch.... I saw the statement    " Also, since this is
a wood framed building I need to sprinkle the Attic"   and based comments on
that. I can't see a daycare being 13R and hence the reason why it is a 13.
Been well my friend hope you as well! 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron
Greenman
Sent: Wednesday, July 17, 2013 8:30 AM
To: [email protected]
Subject: Re: CPVC Applications

Rod, I can't imagine an AHJ calling a daycare 13R. Tell me how it falls into
any R occupancy. I can see him granting a variance to 13 that allows
omission of attic sprinklers if the design goal is life-safety only, but
he's taking a big risk. My read is that daycare, except in that one special
case where it's classified as an E, is a B occupancy and if configured
properly not need a system at all. Not endorsing one thing over the other,
just reading code. And how have you been?


On Wed, Jul 17, 2013 at 7:25 AM, JD Gamble <[email protected]>wrote:

> I believe FlameGuard (Spears) is listed for Low Pressure Dry Systems 
> as well ...
>
> http://spearsmfg.com/**flameguard/FG-3-1010_0113_web.**pdf<http://spea
> rsmfg.com/flameguard/FG-3-1010_0113_web.pdf>
>
> **
> Low Pressure Dry Pipe and Pre-action Systems In accordance with the 
> UL® Listing, Spears® FlameGuard® CPVC Fire Sprinkler Products may be 
> used in Low Pressure Dry Pipe and Pre-action System applications in 
> Light Hazard and Residential occupancies in accordance with NFPA 13, 
> 13D and 13R when subject to the following additional limitations:
> A CPVC Low Pressure Dry Pipe or Pre-action System is a piping system 
> intended for use where piping could be subjected to freezing 
> temperatures and water filled pipe cannot be utilized. The minimum 
> rated temperature is -20° F (-29° C). Low Pressure Dry Pipe systems 
> contain compressed air or nitrogen
> (gas) having an internal gage pressure of not more than 15 psig (105 kPa).
> These specially designed systems require separate control valve 
> mechanisms for this application (supplied by others) that activate to 
> release water into the dry piping section and to the sprinkler heads.
> The water-filled portion of the system control device must be in an 
> area protected from freezing. It is the installer's responsibility to 
> be sure the system is installed in accordance with the limitations of 
> this manual and specifications of a Dry Pipe or Pre-action Fire 
> Sprinkler System design Engineer for proper control devices, pipe 
> sizing, and other important design and maintenance criteria applicable 
> to each project. CPVC dry systems must be designed with the following 
> maximum water delivery time delay.
>
> **
>
>
>
> JD Gamble
> Life Safety Solutions of Sheridan
>
> 307-763-3361
> -----Original Message----- From: Forest Wilson
> Sent: Wednesday, July 17, 2013 8:02 AM
> To: 
> sprinklerforum@lists.**firesprinkler.org<[email protected]
> nkler.org>
> Subject: Re: CPVC Applications
>
>
> I think Tyco has a CPVC listed for use in dry systems?
>
> Sent from my iPhone
>
> On Jul 17, 2013, at 9:52 AM, Rod DiBona <[email protected]> wrote:
>
>  Brian,
>>
>> Don't assume that because you have a wood framed building that you 
>> must sprinkler the attic. Check with the engineer of record to see if 
>> this system is supposed to be a 13 or 13R. Secondly you can't run 
>> over an ordinary hazard room in a light hazard occupancy with cpvc 
>> unless the room is 400 ft or less. And lastly CPVC is not listed for 
>> a dry system and you can definitely not use it. A read of the 
>> blazemaster install and specification manual is highly recommended.
>>
>> Rod at Rapid
>>
>> -----Original Message-----
>> From:
sprinklerforum-bounces@lists.**firesprinkler.org<sprinklerforum-bounces@list
s.firesprinkler.org>[mailto:
>> sprinklerforum-**[email protected].**org<sprinklerforum-bou
>> [email protected]>]
>> On Behalf Of Brian Harris
>> Sent: Wednesday, July 17, 2013 7:43 AM
>> To: 
>> sprinklerforum@lists.**firesprinkler.org<[email protected]
>> inkler.org>
>> Subject: CPVC Applications
>>
>> I'm doing a daycare facility and was leaning towards using 
>> BlazeMaster CPVC but have a quick question. I know that it is listed 
>> and approved for light hazard areas which is 90% of the project, what 
>> do you do for the other 10%? Do I need to run steel for the Kitchen, 
>> Janitor's Closet, and small Storage closet? Also, since this is a 
>> wood framed building I need to sprinkle the Attic but since it cannot 
>> be used for storage it is light hazard as well, any reason I can't use
CPVC for the dry system as well?
>>
>> Brian Harris, CET
>> BVS Systems Inc.
>> Sprinkler Division
>> bvssystemsinc.com<http://**bvssystemsinc.com/
>> <http://bvssystemsinc.com/>
>> >
>> Phone: 704.896.9989
>> Fax: 704.896.1935
>>
>> ______________________________**_________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.**firesprinkler.org<[email protected]
>> inkler.org>
>> http://lists.firesprinkler.**org/listinfo.cgi/**
>> sprinklerforum-firesprinkler.**org<http://lists.firesprinkler.org/lis
>> tinfo.cgi/sprinklerforum-firesprinkler.org>
>>
>> ______________________________**_________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.**firesprinkler.org<[email protected]
>> inkler.org>
>> http://lists.firesprinkler.**org/listinfo.cgi/**
>> sprinklerforum-firesprinkler.**org<http://lists.firesprinkler.org/lis
>> tinfo.cgi/sprinklerforum-firesprinkler.org>
>>
> ______________________________**_________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.**firesprinkler.org<[email protected]
> nkler.org>
> http://lists.firesprinkler.**org/listinfo.cgi/**
> sprinklerforum-firesprinkler.**org<http://lists.firesprinkler.org/list
> info.cgi/sprinklerforum-firesprinkler.org>
> ______________________________**_________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.**firesprinkler.org<[email protected]
> nkler.org>
> http://lists.firesprinkler.**org/listinfo.cgi/**
> sprinklerforum-firesprinkler.**org<http://lists.firesprinkler.org/list
> info.cgi/sprinklerforum-firesprinkler.org>
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to