I believe FlameGuard (Spears) is listed for Low Pressure Dry Systems as well ...

http://spearsmfg.com/flameguard/FG-3-1010_0113_web.pdf

**
Low Pressure Dry Pipe and Pre-action Systems
In accordance with the UL® Listing, Spears® FlameGuard® CPVC Fire Sprinkler
Products may be used in Low Pressure Dry Pipe and Pre-action System
applications in Light Hazard and Residential occupancies in accordance with
NFPA 13, 13D and 13R when subject to the following additional limitations:
A CPVC Low Pressure Dry Pipe or Pre-action System is a piping system
intended for use where piping could be subjected to freezing temperatures and water filled pipe cannot be utilized. The minimum rated temperature is -20° F
(-29° C). Low Pressure Dry Pipe systems contain compressed air or nitrogen
(gas) having an internal gage pressure of not more than 15 psig (105 kPa).
These specially designed systems require separate control valve mechanisms
for this application (supplied by others) that activate to release water into the dry piping section and to the sprinkler heads. The water-filled portion of the system control device must be in an area protected from freezing. It is the installer’s responsibility to be sure the system is installed in accordance with the limitations
of this manual and specifications of a Dry Pipe or Pre-action Fire Sprinkler
System design Engineer for proper control devices, pipe sizing, and other
important design and maintenance criteria applicable to each project. CPVC dry systems must be designed with the following maximum water delivery time delay.

**



JD Gamble
Life Safety Solutions of Sheridan

307-763-3361
-----Original Message----- From: Forest Wilson
Sent: Wednesday, July 17, 2013 8:02 AM
To: [email protected]
Subject: Re: CPVC Applications

I think Tyco has a CPVC listed for use in dry systems?

Sent from my iPhone

On Jul 17, 2013, at 9:52 AM, Rod DiBona <[email protected]> wrote:

Brian,

Don't assume that because you have a wood framed building that you must sprinkler the attic. Check with the engineer of record to see if this system is supposed to be a 13 or 13R. Secondly you can't run over an ordinary hazard room in a light hazard occupancy with cpvc unless the room is 400 ft or less. And lastly CPVC is not listed for a dry system and you can definitely not use it. A read of the blazemaster install and specification manual is highly recommended.

Rod at Rapid

-----Original Message-----
From: [email protected] [mailto:[email protected]] On Behalf Of Brian Harris
Sent: Wednesday, July 17, 2013 7:43 AM
To: [email protected]
Subject: CPVC Applications

I'm doing a daycare facility and was leaning towards using BlazeMaster CPVC but have a quick question. I know that it is listed and approved for light hazard areas which is 90% of the project, what do you do for the other 10%? Do I need to run steel for the Kitchen, Janitor's Closet, and small Storage closet? Also, since this is a wood framed building I need to sprinkle the Attic but since it cannot be used for storage it is light hazard as well, any reason I can't use CPVC for the dry system as well?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to