On Jul 17, 2013, at 9:56 AM, "Brian Harris" <bhar...@bvssystemsinc.com> wrote:

> Thanks Rod, this is a 13 system so the attic needs to be protected. I read 
> what I could find on the BlazeMaster sight but didn't see anything about Dry 
> systems, I'll look again I'm sure I missed it.
> So in the case of the Kitchen for example would you transition to steel for 
> that area and then back to CPVC?
>
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
>
> -----Original Message-----
> From: sprinklerforum-boun...@lists.firesprinkler.org 
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Rod 
> DiBona
> Sent: Wednesday, July 17, 2013 9:52 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: CPVC Applications
>
> Brian,
>
> Don't assume that because you have a wood framed building that you must 
> sprinkler the attic. Check with the engineer of record to see if this system 
> is supposed to be a 13 or 13R. Secondly you can't run over an ordinary hazard 
> room in a light hazard occupancy with cpvc unless the room is 400 ft or less. 
> And lastly CPVC is not listed for a dry system and you can definitely not use 
> it. A read of the blazemaster install and specification manual is highly 
> recommended.
>
> Rod at Rapid
>
> -----Original Message-----
> From: sprinklerforum-boun...@lists.firesprinkler.org 
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brian 
> Harris
> Sent: Wednesday, July 17, 2013 7:43 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: CPVC Applications
>
> I'm doing a daycare facility and was leaning towards using BlazeMaster CPVC 
> but have a quick question. I know that it is listed and approved for light 
> hazard areas which is 90% of the project, what do you do for the other 10%? 
> Do I need to run steel for the Kitchen, Janitor's Closet, and small Storage 
> closet? Also, since this is a wood framed building I need to sprinkle the 
> Attic but since it cannot be used for storage it is light hazard as well, any 
> reason I can't use CPVC for the dry system as well?
>
> Brian Harris, CET
> BVS Systems Inc.
> Sprinkler Division
> bvssystemsinc.com<http://bvssystemsinc.com/>
> Phone: 704.896.9989
> Fax: 704.896.1935
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

________________________________


Both the individual sending this e-mail and The Lubrizol Corporation intend 
that this electronic message be used exclusively by the individual or entity to 
which it is intended to be addressed. This message may contain information that 
is privileged, confidential and thereby exempt and protected from unauthorized 
disclosure under applicable law. If the reader of this message is not the 
intended recipient, or an employee or agent responsible for delivering the 
message to the intended recipient, be aware that any disclosure, dissemination, 
distribution or copying of this communication, or the use of its contents, is 
not authorized and is strictly prohibited. If you have received this 
communication and are not the intended recipient, please notify the sender 
immediately and permanently delete the original message from your e-mail system.
http://online.lubrizol.com/disclaimer/cliquez_ici_pour_traduction_en_francais.htm
http://online.lubrizol.com/disclaimer/Klicken_Sie_hier_fur_die_deutsche_Ubersetzung.htm
http://online.lubrizol.com/disclaimer/Clicar_aqui_para_versao_em_Portugues.htm
http://online.lubrizol.com/disclaimer/De_un_clic_aqui_para_su_traduccion_al_espanol.htm
http://online.lubrizol.com/disclaimer/Chinese.htm
http://online.lubrizol.com/disclaimer/Japanese.htm


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to