Thanks Rod, this is a 13 system so the attic needs to be protected. I read what 
I could find on the BlazeMaster sight but didn't see anything about Dry 
systems, I'll look again I'm sure I missed it.
So in the case of the Kitchen for example would you transition to steel for 
that area and then back to CPVC?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Rod DiBona
Sent: Wednesday, July 17, 2013 9:52 AM
To: [email protected]
Subject: RE: CPVC Applications

Brian,

Don't assume that because you have a wood framed building that you must 
sprinkler the attic. Check with the engineer of record to see if this system is 
supposed to be a 13 or 13R. Secondly you can't run over an ordinary hazard room 
in a light hazard occupancy with cpvc unless the room is 400 ft or less. And 
lastly CPVC is not listed for a dry system and you can definitely not use it. A 
read of the blazemaster install and specification manual is highly recommended.

Rod at Rapid

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brian 
Harris
Sent: Wednesday, July 17, 2013 7:43 AM
To: [email protected]
Subject: CPVC Applications

I'm doing a daycare facility and was leaning towards using BlazeMaster CPVC but 
have a quick question. I know that it is listed and approved for light hazard 
areas which is 90% of the project, what do you do for the other 10%? Do I need 
to run steel for the Kitchen, Janitor's Closet, and small Storage closet? Also, 
since this is a wood framed building I need to sprinkle the Attic but since it 
cannot be used for storage it is light hazard as well, any reason I can't use 
CPVC for the dry system as well?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to