"So in the case of the Kitchen for example would you transition to steel
for that area and then back to CPVC?"

Yes, we do it all the time. I like to arrange the piping to limit the
transitions.


David Autry

Meininger Fire Protection Inc.
2521 W L St. Suite No.4
Lincoln, Ne 68522
Voice (402) 466-2616
Fax (402) 466-2617
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian
Harris
Sent: Wednesday, July 17, 2013 8:56 AM
To: [email protected]
Subject: RE: CPVC Applications

Thanks Rod, this is a 13 system so the attic needs to be protected. I read
what I could find on the BlazeMaster sight but didn't see anything about
Dry systems, I'll look again I'm sure I missed it.
So in the case of the Kitchen for example would you transition to steel
for that area and then back to CPVC?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rod
DiBona
Sent: Wednesday, July 17, 2013 9:52 AM
To: [email protected]
Subject: RE: CPVC Applications

Brian,

Don't assume that because you have a wood framed building that you must
sprinkler the attic. Check with the engineer of record to see if this
system is supposed to be a 13 or 13R. Secondly you can't run over an
ordinary hazard room in a light hazard occupancy with cpvc unless the room
is 400 ft or less. And lastly CPVC is not listed for a dry system and you
can definitely not use it. A read of the blazemaster install and
specification manual is highly recommended.

Rod at Rapid

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian
Harris
Sent: Wednesday, July 17, 2013 7:43 AM
To: [email protected]
Subject: CPVC Applications

I'm doing a daycare facility and was leaning towards using BlazeMaster
CPVC but have a quick question. I know that it is listed and approved for
light hazard areas which is 90% of the project, what do you do for the
other 10%? Do I need to run steel for the Kitchen, Janitor's Closet, and
small Storage closet? Also, since this is a wood framed building I need to
sprinkle the Attic but since it cannot be used for storage it is light
hazard as well, any reason I can't use CPVC for the dry system as well?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to