It is generally prudent to start with the official occupancy classification(s) 
indicated by the Architect and agreed upon by the Building Official... when 
determining whether anything less than an NFPA 13 system is allowed.  

This is because even if the building is within the scope of NFPA 13R, an NFPA 
13 system may be required by a building's design due to the Architect designing 
the building to take credit for IBC exceptions for which only an NFPA 13 system 
is allowed.  

There is a very good table in the 2006 IBC Commentary version illustrating 
"Examples of Requirements Modified Through Use of Automatic Sprinkler Systems" 
[Figure 903.3.1.1(2)].  It compared NFPA 13/13R/13D and illustrated the 
differences such as with IBC 506.3 [area increase] which only an NFPA 13 system 
could give you.  It showed other similar "NFPA 13 only" situations for 
qualification for Rating Reductions such as found in 508.3.3, Table 601, and 
708.3.


Respectfully,


David W. S. Blackwell, II, PE, CFPE, CFI I
Chief Engineer
Office of State Fire Marshal
SC Department of Labor, Licensing, & Regulation, 141 Monticello Trail, 
Columbia, SC 29203
Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
Fax: 803.896.9806 [Office]
Email:   [email protected]
Website:  http://www.scfiremarshal.llronline.com/


Please note that you can sign up to receive automatic information on SC 
Division of Fire and Life Safety current events, policies, laws and procedures 
by visiting our Web site at:  http://www.scfiremarshal.llronline.com/


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Mark A. 
Sornsin, P.E.
Sent: Wednesday, July 17, 2013 12:41 PM
To: [email protected]
Subject: RE: CPVC Applications

Whoohh - Save your breath, fella.

Child care facilities (under the IBC anyway) fall into an I-4 classification. 
There is an exception that kicks them into an "E" classification; and there is 
a Day Care facility exception for 5 or fewer persons that kicks you into R-3.  
But otherwise Day Care or Child Care are to be classified I-4.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ron 
Greenman
Sent: Wednesday, July 17, 2013 9:30 AM
To: [email protected]
Subject: Re: CPVC Applications

Rod, I can't imagine an AHJ calling a daycare 13R. Tell me how it falls into 
any R occupancy. I can see him granting a variance to 13 that allows omission 
of attic sprinklers if the design goal is life-safety only, but he's taking a 
big risk. My read is that daycare, except in that one special case where it's 
classified as an E, is a B occupancy and if configured properly not need a 
system at all. Not endorsing one thing over the other, just reading code. And 
how have you been?


On Wed, Jul 17, 2013 at 7:25 AM, JD Gamble <[email protected]>wrote:

> I believe FlameGuard (Spears) is listed for Low Pressure Dry Systems 
> as well ...
>
> http://spearsmfg.com/**flameguard/FG-3-1010_0113_web.**pdf<http://spea
> rsmfg.com/flameguard/FG-3-1010_0113_web.pdf>
>
> **
> Low Pressure Dry Pipe and Pre-action Systems In accordance with the 
> UL® Listing, Spears® FlameGuard® CPVC Fire Sprinkler Products may be 
> used in Low Pressure Dry Pipe and Pre-action System applications in 
> Light Hazard and Residential occupancies in accordance with NFPA 13, 
> 13D and 13R when subject to the following additional limitations:
> A CPVC Low Pressure Dry Pipe or Pre-action System is a piping system 
> intended for use where piping could be subjected to freezing 
> temperatures and water filled pipe cannot be utilized. The minimum 
> rated temperature is -20° F (-29° C). Low Pressure Dry Pipe systems 
> contain compressed air or nitrogen
> (gas) having an internal gage pressure of not more than 15 psig (105 kPa).
> These specially designed systems require separate control valve 
> mechanisms for this application (supplied by others) that activate to 
> release water into the dry piping section and to the sprinkler heads.
> The water-filled portion of the system control device must be in an 
> area protected from freezing. It is the installer's responsibility to 
> be sure the system is installed in accordance with the limitations of 
> this manual and specifications of a Dry Pipe or Pre-action Fire 
> Sprinkler System design Engineer for proper control devices, pipe 
> sizing, and other important design and maintenance criteria applicable 
> to each project. CPVC dry systems must be designed with the following 
> maximum water delivery time delay.
>
> **
>
>
>
> JD Gamble
> Life Safety Solutions of Sheridan
>
> 307-763-3361
> -----Original Message----- From: Forest Wilson
> Sent: Wednesday, July 17, 2013 8:02 AM
> To:
> sprinklerforum@lists.**firesprinkler.org<[email protected]
> nkler.org>
> Subject: Re: CPVC Applications
>
>
> I think Tyco has a CPVC listed for use in dry systems?
>
> Sent from my iPhone
>
> On Jul 17, 2013, at 9:52 AM, Rod DiBona <[email protected]> wrote:
>
>  Brian,
>>
>> Don't assume that because you have a wood framed building that you 
>> must sprinkler the attic. Check with the engineer of record to see if 
>> this system is supposed to be a 13 or 13R. Secondly you can't run 
>> over an ordinary hazard room in a light hazard occupancy with cpvc 
>> unless the room is 400 ft or less. And lastly CPVC is not listed for 
>> a dry system and you can definitely not use it. A read of the 
>> blazemaster install and specification manual is highly recommended.
>>
>> Rod at Rapid
>>
>> -----Original Message-----
>> From: 
>> sprinklerforum-bounces@lists.**firesprinkler.org<[email protected]>[mailto:
>> sprinklerforum-**[email protected].**org<sprinklerforum-bou
>> [email protected]>]
>> On Behalf Of Brian Harris
>> Sent: Wednesday, July 17, 2013 7:43 AM
>> To:
>> sprinklerforum@lists.**firesprinkler.org<[email protected]
>> inkler.org>
>> Subject: CPVC Applications
>>
>> I'm doing a daycare facility and was leaning towards using 
>> BlazeMaster CPVC but have a quick question. I know that it is listed 
>> and approved for light hazard areas which is 90% of the project, what 
>> do you do for the other 10%? Do I need to run steel for the Kitchen, 
>> Janitor's Closet, and small Storage closet? Also, since this is a 
>> wood framed building I need to sprinkle the Attic but since it cannot 
>> be used for storage it is light hazard as well, any reason I can't use CPVC 
>> for the dry system as well?
>>
>> Brian Harris, CET
>> BVS Systems Inc.
>> Sprinkler Division
>> bvssystemsinc.com<http://**bvssystemsinc.com/
>> <http://bvssystemsinc.com/>
>> >
>> Phone: 704.896.9989
>> Fax: 704.896.1935
>>
>> ______________________________**_________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.**firesprinkler.org<[email protected]
>> inkler.org>
>> http://lists.firesprinkler.**org/listinfo.cgi/**
>> sprinklerforum-firesprinkler.**org<http://lists.firesprinkler.org/lis
>> tinfo.cgi/sprinklerforum-firesprinkler.org>
>>
>> ______________________________**_________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.**firesprinkler.org<[email protected]
>> inkler.org>
>> http://lists.firesprinkler.**org/listinfo.cgi/**
>> sprinklerforum-firesprinkler.**org<http://lists.firesprinkler.org/lis
>> tinfo.cgi/sprinklerforum-firesprinkler.org>
>>
> ______________________________**_________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.**firesprinkler.org<[email protected]
> nkler.org>
> http://lists.firesprinkler.**org/listinfo.cgi/**
> sprinklerforum-firesprinkler.**org<http://lists.firesprinkler.org/list
> info.cgi/sprinklerforum-firesprinkler.org>
> ______________________________**_________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.**firesprinkler.org<[email protected]
> nkler.org>
> http://lists.firesprinkler.**org/listinfo.cgi/**
> sprinklerforum-firesprinkler.**org<http://lists.firesprinkler.org/list
> info.cgi/sprinklerforum-firesprinkler.org>
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to