Well, now that you two have hijacked my thread.... This was a question
about philosophy and history, not math and time. Let's try again, and the
bathroom compartmentalization thread is similar to what I'd like some
feedback on.

Most discussion about spacing rules revolve around arguments relating to
distribution. I'm wondering how many are based on heat detection.

For instance, why can I use an XYZ SSP head to cover 225 sq in light hazard
but not ordinary. Since I'm after density over square footage I can
certainly accomplish this prohibited feat. But after a given edition we are
suddenly required to use QR heads for light hazard for some unspecified
reason. That certainly doesn't have anything to do with coverage.


On Thu, Oct 3, 2013 at 10:11 AM, Brad Casterline <[email protected]>wrote:

> Yes, and by 'different fire curves' I assume you mean fire growth rates.
> I want to model the four common 'design fires': SLOW, MEDIUM, FAST, and
> ULTRAFAST. All four will be "T-Squared", which as you know means the growth
> is proportional to the time squared. I am not sure what the proper word is
> for the factor that distinguishes SLOW from FAST but I know what the
> numbers
> are and how to calc how many seconds from ignition to peak RHR (Rate of
> Heat
> Release). I want to find out what this "...same RHR point..." is. I will
> have to run (8) scenarios because I want to use two separate max RHR. I
> will
> use 1250 kW and 2500 kW. The factor I use for FAST, for example, is .0466
> kW/sec2. So a 2500 kW T-Squared FAST fire would peak at
> (2500/.0466)^.5=~232
> seconds. I suppose I could then compare the activation time to the time for
> max RHR and get a percent before or after for the different growth rates
> and
> max RHRs.
> thanks,
> Brad
>
> -----Original Message-----
> From: Roland Huggins [mailto:[email protected]]
> Sent: Thursday, October 03, 2013 10:57 AM
> To: [email protected]
> Subject: Re: Spacing Rules
>
> I was simply trying to make the reference to time more than just how many
> seconds have passed and tie it to the level of hazard presented by the fire
> by using the same point on the different fire curves.
>
> Roland
>
>
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
>
>
>
>
>
> On Oct 3, 2013, at 5:54 AM, Brad Casterline <[email protected]>
> wrote:
>
> > Dang Roland this opens up a whole new can of curiosity for me.
> > Figuring out exactly what you mean will give me something to do the next
> > couple-three lunch breaks. I usually check out the FDS-SMV discussions
> but
> > for some dumba$$ reason the NIST site has been down since Tuesday (smh).
> >
> > Brad
> > ****************
> > ..... A more meaningful reference for activation is in regard to the same
> > RHR point for the different fire curves......
> >
> > ......
> > Roland
> >
> > Roland Huggins, PE - VP Engineering
> > American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> > Dallas, TX
> > http://www.firesprinkler.org
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to