The question Brad, is,  what is the history of where each of those applied
to the development of what rules. Obviously flow rate has nothing to do
with detection spacing, but response time does and that may influence
density. I do know that once there was no light hazard and then one cycle
there was. And that for ever so long I could space to a max of 225 sqft
under certain circumstances with standard spray/standard response heads.
Then towards the end of the last century or the beginning of this I had to
use quick response. I presume there was something that influenced this
change and it wasn't money because SR and QR cost the same and if it were
money it should have revolved around the density being insufficient. That
would have promulgated closer spacing or greater flow rates which would
have increased the sale of materials. Not money. Fire growth rates in LH
occupancies may have quickened and then the way to deal with that would be
quicker response. I can get that with QR heads or closer detection spacing.
Now I'm just speculating. If I knew I'd be expostulating, if not
pontificating, and not questioning.


On Fri, Oct 4, 2013 at 6:25 AM, Brad Casterline <[email protected]>wrote:

> Sorry about that Ron, I get carried away. I should have stopped with
> '...paradox...', since it addressed spacing and detection.
> It is pretty hard to leave time out of battling accidental fires though, it
> being of the utmost importance, so we have flow rates, heat release rates,
> response time index...
>
> Brad
>
> -----Original Message-----
> From: rongreenman . [mailto:[email protected]]
> Sent: Thursday, October 03, 2013 8:50 PM
> To: [email protected]
> Subject: Re: Spacing Rules
>
> Well, now that you two have hijacked my thread.... This was a question
> about philosophy and history, not math and time. Let's try again, and the
> bathroom compartmentalization thread is similar to what I'd like some
> feedback on.
>
> Most discussion about spacing rules revolve around arguments relating to
> distribution. I'm wondering how many are based on heat detection.
>
> For instance, why can I use an XYZ SSP head to cover 225 sq in light hazard
> but not ordinary. Since I'm after density over square footage I can
> certainly accomplish this prohibited feat. But after a given edition we are
> suddenly required to use QR heads for light hazard for some unspecified
> reason. That certainly doesn't have anything to do with coverage.
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to