Todd,
I would consider this a Platform and apply 8.15.6, 2010 ed.
Regards,
G. Tim Stone
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638 TEL: (802) 434-2968 Fax: (802) 434-4343
[email protected]
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
Steven
> Scandaliato
> Sent: Tuesday, January 07, 2014 4:20 PM
> To: [email protected]
> Subject: RE: concealed space definition
>
> Today...it is whatever you and the AHJ agree on. Hopefully (fingers
> crossed) we will have a clear definition in the next edition as we are
> working at adding the "gaps and clouds" section and with this will come
new
> definitions including concealed spaces and the 4ft rule. Hold your
breath!
> Haha.
>
> Steven Scandaliato, SET CFPS
> 520.971.2322 Cell
> Skype: steven.scandaliato
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Todd
-
> Work
> Sent: Tuesday, January 07, 2014 3:12 PM
> To: [email protected]
> Subject: concealed space definition
>
> Is there an official definition of a concealed space? Is a 10 ft x 20 ft
> platform that is 9" off the ground but not enclosed on the sides
considered
> a concealed space?
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> 860-535-2080 (ofc)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
> firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
> firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org