Even better. Pretty humid environment.

On Wed, Jan 8, 2014 at 1:46 PM, Todd - Work <[email protected]> wrote:

> Actually they are going to be growing medical marijuana.
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> 860-535-2080 (ofc)
>
> > On Jan 8, 2014, at 4:33 PM, "rongreenman ." <[email protected]>
> wrote:
> >
> > Sounds like a growing mushroom house.
> >
> >
> >> On Wed, Jan 8, 2014 at 9:30 AM, Todd - Work <[email protected]> wrote:
> >>
> >> Each 40 ft x 64 ft room in this area has six 9 ft x 20 ft tables,
> spaced 1
> >> ft apart in one direction and 3 ft apart in the other. Agricultural
> >> occupancy so OH2 design. Tables are not skirted. In addition to wood
> >> construction, there will be plastic sheeting and plastic tubing under
> the
> >> table. (I am using the term "table" because that is what they call
> them).
> >> It will be a wet environment by nature of the occupancy.
> >>
> >> One interesting semantic note is that 11.2.3.1.8 (3), which is the 3000
> >> sqft requirement, references 8.14.6, which is the platform requirement
> also
> >> references combustible concealed spaces. But 8.14.6 only references
> >> combustible spaces. Nothing about them being concealed
> >>
> >> Looking at this from a practical perspective (think like fire), if a
> fire
> >> did start under a table, it could have significant time to develop
> before
> >> being detected. There may not be enough heat generated to activate a
> >> sprinkler until after it is well developed. Perhaps not until flames
> >> actually shoot up around the edge of the table. If flames shoot up
> around
> >> more than one side of the table (possible in a 9x20 table), then a lot
> of
> >> sprinklers over a fairly large area could open. More than would be
> included
> >> in a 1500 sqft area? Potentially. This is where my thought for the 3000
> >> sqft area comes from. (FWIW, EH2 occupancy description also references
> >> shielded fires).
> >>
> >> As for liability, the nature of our society is that we need to consider
> >> this as well as the technical aspect of our job.
> >>
> >>
> >> Todd G Williams, PE
> >> Fire Protection Design/Consulting
> >> Stonington, CT
> >> www.fpdc.com
> >> 860-535-2080 (ofc)
> >>
> >>> On Jan 8, 2014, at 11:23 AM, "Brad Casterline" <
> [email protected]>
> >> wrote:
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to