NFPA 73-2006 3.3.6 (partial):

Concealed:
Rendered inaccessible by the structure or finish of the building.

brad

-----Original Message-----
From: John Denhardt [mailto:[email protected]] 
Sent: Tuesday, January 07, 2014 4:56 PM
To: <[email protected]>
Subject: Re: concealed space definition

I fully agree based on the 2013 edition. 

Thanks,
John August Denhardt P.E.

> On Jan 7, 2014, at 4:26 PM, "G. Tim Stone" <[email protected]> wrote:
> 
> Todd,
> 
> I would consider this a Platform and apply 8.15.6, 2010 ed.
> 
> Regards,
> G. Tim Stone
> 
> G. Tim Stone Consulting, LLC
> NICET Level III Engineering Technician
> Fire Protection Sprinkler Design
> and Consulting Services
> 
>                117 Old Stage Rd. - Essex Jct., VT. 05452
> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
>                           [email protected]
> 
> 
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of
> Steven
>> Scandaliato
>> Sent: Tuesday, January 07, 2014 4:20 PM
>> To: [email protected]
>> Subject: RE: concealed space definition
>> 
>> Today...it is whatever you and the AHJ agree on.  Hopefully (fingers
>> crossed) we will have a clear definition in the next edition as we are
>> working at adding the "gaps and clouds" section and with this will come
> new
>> definitions including concealed spaces and the 4ft rule.  Hold your
> breath!
>> Haha.
>> 
>> Steven Scandaliato, SET CFPS
>> 520.971.2322 Cell
>> Skype: steven.scandaliato
>> 
>> 
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Todd
> -
>> Work
>> Sent: Tuesday, January 07, 2014 3:12 PM
>> To: [email protected]
>> Subject: concealed space definition
>> 
>> Is there an official definition of a concealed space? Is a 10 ft x 20 ft
>> platform that is 9" off the ground but not enclosed on the sides
> considered
>> a concealed space?
>> 
>> Todd G Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> www.fpdc.com
>> 860-535-2080 (ofc)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
>> firesprinkler.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
>> firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to