Risk category is a term established in the 2010 edition of ASCE7, and is defined in Table 1.5-1 of that document. If your documents establish it as III, here's the examples from ASCE7:

Buildings and other structures not included in Risk Category IV (including, but not limited to, facilities that manufacture, process, handle, store, use, or dispose of such substances as hazardous fuels, hazardous chemicals, hazardous waste, or explosives) containing toxic or explosive substances where their quantity exceeds a threshold quantity established by the authority having jurisdiction and is suffi cient to pose a threat to the public if released.

For purposes of determining the seismic design category it's irrelevant whether the risk category is I-II-III.

What really nails this down, as Steve Leyton noted, is the Ss value for the site, which is established by the location of the building in a seismic zone. If you have the site latitude and longitude (easily obtained from various sources) the Ss value can be determined from the USGS, at:

http://geohazards.usgs.gov/designmaps/us/application.php

I would only start this process myself to have some guidelines prior to asking the building structural to establish the seismic design category.

This above is not a Formal Interpretation issued pursuant to NFPA Regulations. Any opinion expressed is the personal opinion of the author and does not necessarily represent the official position of the NFPA or its Technical Committees. In addition, this correspondence is neither intended, nor should it be relied upon, to provide professional consultation or services.
*

PARSLEY CONSULTING

*Ken Wagoner
760.745.6181 voice
760.745.0537 fax

website: www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>
On 1/23/2014 9:14 AM, Richard Mote wrote:
RFI time, the specifications call for bracing. I was tasked with finding out if 
bracing is indeed required. I've wasted enough of my time and the forums time.
The structural sheet calls it;
Risk Category III
Seismic Importance Factor 1.25
There are places for about 10 more line of information but they all have X's 
where there should be data.


Richard L. Mote
Rowe Sprinkler Systems, Inc.

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve 
Leyton
Sent: Thursday, January 23, 2014 11:56 AM
To: [email protected]
Subject: RE: Fredrick MD, Seismic Zone?

Right.  Provisions for seismic protection of buildings and building systems in 
the IBC and also in NFPA 13 are now all based on ASCE 7.  We rolled a new code 
on 1/1/14, so moved forward to ASCE 7, 2010 here in
CA.   ASCE standards establish parameters for when a building is
required to be seismically engineered.   The structural engineer of
record for a given project is usually charged - sometimes in conjunction with 
the soils engineer - with determining whether a particular parcel is subject to 
those provisions.  As Travis says, seismic has changed; IMHO, it's not for the 
sprinkie to determine if seismic protection is required, only to verify with 
the SEOR or through the construction documents whether or not it's required.

Steve Leyton




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis Mack
Sent: Thursday, January 23, 2014 8:42 AM
To: [email protected]
Subject: Re: Fredrick MD, Seismic Zone?

Seismic has changed DRASTICALLY from what we used to do.  The SE will have to 
provide you the structural design category and the Ss for the project.  
Hopefully it is SDC of A or B and you don't have to worry about anything.

But, it is definitely no longer 40' / 80' and 4 way every change in direction.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

On 1/23/2014 9:38 AM, Richard Mote wrote:
Structural design notes sheet is no help, we are sending an RFI for
clarification. I haven't  had to worry about seismic locally for about
10.5 years so I am not as well versed as I should be.
Richard L. Mote
Rowe Sprinkler Systems, Inc.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Travis Mack
Sent: Thursday, January 23, 2014 11:17 AM
To: [email protected]
Subject: Re: Fredrick MD, Seismic Zone?

What does the structural design notes sheet provide?  Is it Seismic
Category C or higher.  If so, bracing is required on fire sprinkler systems.  I 
don't think the seismic maps really apply any longer.  You need to know the 
Seismic Design Category, then you need the Ss values so you can calculate your 
bracing.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

On 1/23/2014 9:15 AM, Richard Mote wrote:
Can someone with experience in the area tell me if Seismic bracing is
required in Fredrick Maryland? (21701) According to the maps I found online at 
appears to be the same seismic category as central PA, but not having worked in 
the area before I wanted to be sure there wasn't some local requirement.
Richard L. Mote
Rowe Sprinkler Systems, Inc.
7994 Route 522, Suite 1
PO Box 407
Middleburg, PA 17842
P 570-837-7647
F 570-837-6335

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
l
er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to