OH1 Parking garage. Ron F -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Roland Huggins Sent: Tuesday, February 18, 2014 2:22 PM To: [email protected] Subject: Re: Static Pressure/Working Pressure
IT is referring to the surge pressures running through the distribution system. The non flowing churn pressure fits right in the definition. The problem is not one of potential rupture etc but of liability of knowingly exceeding the preassigned line in the sand. What's the occupancy classification for the lower areas where you are at 178 psi? Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Feb 18, 2014, at 1:10 PM, [email protected] wrote: > 3.3.23 ('13) System working pressure. The maximum anticipated static > (nonnflowing) or flowing pressure applied to the sprinkler system components > exclusive of surge pressures and exclusive of pressure from the fire > department connection. Isn't the occasional test run of an electric pump a > "surge pressure"? > Ron F _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org