Don,

Service sizing is an interesting affair.  When people ask for a 200 amp
service they are speaking of normal load,  as anyone who's ever studied
arc-faults knows a 200 amp service in close proximity to a transformer will
easily deliver short circuit currents in excess of 200 amps, how much you
ask, how about 20, 30, 40 THOUSAND Amps, yes as in 40,000.  This is why the
code requires the interrupting capacity of over current circuit devices to
be equal to or greater than the short circuit current. Hence why circuit
breakers also carry an Interrupting rating which is the available short
circuit current (ASCC), usually breakers are marked with a yellow dot/star
decal with the rating, 10K, 22K, etc.  

The calculation is ASCC = TFLC (Total Full Load Current) / Z (Impendence),
for example 241A/.015 = 16,067A    This is also the reason fire pump
controllers are SUSE Rated (SUITABLE for USE as SERVICE EQUIPMENT)  So as
you can see a service will deliver a hell of lot more than the nominal size
of the service.

Ok back to the service,  the service conductors are only required to be
sized for 125% of Full Load Current, yet the overcurrent devices are
required to be sized at Locked Rotor Current typically 600%. That's the
reason you see these 400 A, 600A, 800A OCPD Disconnects to accommodate the
circuit breaker which is sized at locked rotor current.   Locked Rotor
Indefinitely, let's see how long those 125% feeders last in raceway at 600%
(475% greater than they were sized for). The whole idea is to be sure a
circuit breaker or fuse isn't going to trip should the motor start slow
building counter emf, under heavy load or dragging its armature....run to
destruction, including setting the feeder conductors afire.

Check with your Utility and see how they want the service sized explaining
it's a NEC 695 Fire Pump, give them 125% (continuous load) of FLC and the
LRC, etc.  Last but not least the  fire pump service should only carry the
controller and the pump.  The rest of the stuff including the jockey goes on
general purpose or emergency if they choose but not the fire pump service or
fire pump transfer switch. I know 695 talks about calcs for pressure
maintenance pumps and accessories but see what 695 covers and does not
cover. (NEC 696.1(A) and (B)

Hope that helps,

John Drucker, CET
Assistant Construction Official
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Red Bank, New Jersey



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Don
Lowry
Sent: Saturday, April 5, 2014 1:11 PM
To: [email protected]
Subject: Fire Pump Electrical Service

References from NFPA-20 (2010 edition) 

Situation:

Fire Pump to be installed on ESFR system  (75 hp) electric motor.
9.2.2 (1) or (5)

On down through Chapter 9  to;

9.2.3.4 Where the overcurrent protection permitted by 9.2.3 is installed,
the overcurrent protection device shall be rated to carry indefinitely the
sum of the locked rotor current of the fire pump motor(s) and the pressure
maintenance pump motor(
s) and the full-load current of the associated fire pump accessory
equipment.

OK, so the locked rotor current is 543 amps, plus jockey pump, lights, heat,
etc added would require a 600 amp over current protective device.  This is
what the Engineer and I determined would be the requirement for this
dedicated service to the fire pump.

When the engineer submitted his electrical service plan (600 amp service) to
the city, the City Plan Reviewer states that we don't need a 600 amp
service, but rather a 125 amp service.

In reading through Article 695.4 of the NEC. It states:
 "Where the locked rotor current value does not correspond to a standard
overcurrent device size, the next standard overcurrent device size shall be
used in accordance with 240.6.  The requirement to carry the locked rotor
currents indefinitely shall not apply to conductors or devices other than
overcurrent devices in the fire pump motor circuits." 

So, does this mean that the service itself (transformer) and related
conductors can be per normal size (125 amp) with just a 600 amp fuse in the
disconnect before the controller?

In 30 + years this is the first time I have ever been asked about this.
Before I was only asked about pump size etc , and when installed and checked
at pump start-up there was indeed a fuse of appropriate size in the service
disconnect.  So I assumed all was correct.  I'm just wanting to make sure
the Engineer and I understand the requirements for the actual electrical
service provided.  I know it's not my area of expertise, nor my
responsibility, just curious.

Thanks in advance for any help.

Don Lowry, CET, RME (TX)











_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to