Don,

Service sizing is an interesting affair.  When people ask for a 200 amp service 
they are speaking of normal load,  as anyone who's ever studied arc-faults 
knows a 200 amp service in close proximity to a transformer will easily deliver 
short circuit currents in excess of 200 amps, how much you ask, how about 20, 
30, 40 THOUSAND Amps, yes as in 40,000.  This is why the code requires the 
interrupting capacity of over current circuit devices to be equal to or greater 
than the short circuit current. Hence why circuit breakers also carry an 
Interrupting rating which is the available short circuit current (ASCC), 
usually breakers are marked with a yellow dot/star decal with the rating, 10K, 
22K, etc.  

The calculation is ASCC = TFLC (Total Full Load Current) / Z (Impendence),
for example 241A/.015 = 16,067A    This is also the reason fire pump
controllers are SUSE Rated (SUITABLE for USE as SERVICE EQUIPMENT)  So as you 
can see a service will deliver a hell of lot more than the nominal size of the 
service.

Ok back to the service,  the service conductors are only required to be sized 
for 125% of Full Load Current, yet the overcurrent devices are required to be 
sized at Locked Rotor Current typically 600%. That's the reason you see these 
400 A, 600A, 800A OCPD Disconnects to accommodate the
circuit breaker which is sized at locked rotor current.   Locked Rotor
Indefinitely, let's see how long those 125% feeders last in raceway at 600% 
(475% greater than they were sized for). The whole idea is to be sure a circuit 
breaker or fuse isn't going to trip should the motor start slow building 
counter emf, under heavy load or dragging its armature....run to destruction, 
including setting the feeder conductors afire.

Check with your Utility and see how they want the service sized explaining it's 
a NEC 695 Fire Pump, give them 125% (continuous load) of FLC and the LRC, etc.  
Last but not least the  fire pump service should only carry the controller and 
the pump.  The rest of the stuff including the jockey goes on general purpose 
or emergency if they choose but not the fire pump service or fire pump transfer 
switch. I know 695 talks about calcs for pressure maintenance pumps and 
accessories but see what 695 covers and does not cover. (NEC 696.1(A) and (B)

Hope that helps,

John Drucker, CET
Assistant Construction Official
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Red Bank, New Jersey



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Don Lowry
Sent: Saturday, April 5, 2014 1:11 PM
To: [email protected]
Subject: Fire Pump Electrical Service

References from NFPA-20 (2010 edition) 

Situation:

Fire Pump to be installed on ESFR system  (75 hp) electric motor.
9.2.2 (1) or (5)

On down through Chapter 9  to;

9.2.3.4 Where the overcurrent protection permitted by 9.2.3 is installed, the 
overcurrent protection device shall be rated to carry indefinitely the sum of 
the locked rotor current of the fire pump motor(s) and the pressure maintenance 
pump motor(
s) and the full-load current of the associated fire pump accessory equipment.

OK, so the locked rotor current is 543 amps, plus jockey pump, lights, heat, 
etc added would require a 600 amp over current protective device.  This is what 
the Engineer and I determined would be the requirement for this dedicated 
service to the fire pump.

When the engineer submitted his electrical service plan (600 amp service) to 
the city, the City Plan Reviewer states that we don't need a 600 amp service, 
but rather a 125 amp service.

In reading through Article 695.4 of the NEC. It states:
 "Where the locked rotor current value does not correspond to a standard 
overcurrent device size, the next standard overcurrent device size shall be 
used in accordance with 240.6.  The requirement to carry the locked rotor 
currents indefinitely shall not apply to conductors or devices other than 
overcurrent devices in the fire pump motor circuits." 

So, does this mean that the service itself (transformer) and related conductors 
can be per normal size (125 amp) with just a 600 amp fuse in the disconnect 
before the controller?

In 30 + years this is the first time I have ever been asked about this.
Before I was only asked about pump size etc , and when installed and checked at 
pump start-up there was indeed a fuse of appropriate size in the service 
disconnect.  So I assumed all was correct.  I'm just wanting to make sure the 
Engineer and I understand the requirements for the actual electrical service 
provided.  I know it's not my area of expertise, nor my responsibility, just 
curious.

Thanks in advance for any help.

Don Lowry, CET, RME (TX)











_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to