8.6.1.1.3.1 says that where there is more than one source of water
supply there shall be a check valve installed on each connection.   But
don't forget that 8.16.1.1.3.5 also says you're to have control valves
on both sides of that check valve, but there are exceptions which may or
may not affect the arrangement.   As far as putting a check valve on
each individual system, I don't think it's a requirement and with small
diameter "systems" of 2-3 sprinklers each, it's arguably a bad idea
because such small volume piping networks will be unusually sensitive to
pressure packing from surges and thermal expansion.    Are the risers
furnished with relief valves?

Steve L.




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Aaron Peck
Sent: Tuesday, April 08, 2014 5:21 AM
To: [email protected]
Subject: System Check Valve

Hey group, this may be a dumb question but does a sprinkler system
"need" a check valve?

I have a situation where there's several containerized housing side by
side. Each container has it independent lead in and riser.

None of the risers have check valves, only a valve, flow switch and
test/drain valve. I'm doing an inspection and I'm not sure IF check
valves are necessary. I can't find anything in the code explicitly
stating it needs one.

Since it's feed from one source, I'm checking for a main check valve/
back flow now, and since it's more of a horizontal multi-story building
lol only 2 or 3 heads per floor. I don't think it's required.

And besides just acting as a valve to prevent water leaving the system
piping, I can't remember any other reason.

Sent from my iPhone
Aaron M. Peck, SET Fire Protection
Skype +1(202)407-9079
Cambodia +855(0)78700407
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to