Mixed some 13 and some 13R. Mostly office and housing containers. There's 1 
kitchen located in a double wide container and 1 single container washer/dryer.

Sent from my iPhone
Aaron M. Peck, SET Fire Protection
Skype +1(202)407-9079
Cambodia +855(0)78700407

> On Apr 8, 2014, at 5:39 PM, Ed Kramer <[email protected]> wrote:
> 
> What is the design standard - 13, 13R, or 13D?
> 
> Ed Kramer
> Lawrence, KS
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Aaron
> Peck
> Sent: Tuesday, April 08, 2014 9:37 AM
> To: [email protected]
> Subject: Re: System Check Valve
> 
> It's a system acceptance.
> 
> A FDC is another valid point but the circumstances may be an over riding
> factor.
> 
> I'm was going to ask the AHJ about that but haven't until I'm able to go
> through the whole job.
> 
> There's another thing, the containers are connected to the underground via a
> black plastic pipe aboveground. I'm getting the submittals on that pipe
> tomorrow. And the underground has no way to be flushed or a pressure gauge
> on the underground to do a pressure test.
> 
> Just another day and another project.
> 
> 
> 
> Sent from my iPhone
> Aaron M. Peck, SET Fire Protection
> Skype +1(202)407-9079
> Cambodia +855(0)78700407
> 
>>> On Apr 8, 2014, at 4:45 PM, John Denhardt <[email protected]>
>> wrote:
>> 
>> What type of inspection are you performing; NFPA 25 or system acceptance
> per NFPA 13?
>> 
>> John
>> 
>> John August Denhardt, P.E., FSFPE
>> Strickland Fire Protection Incorporated
>> 5113 Berwyn Road
>> College Park, Maryland 20740
>> Office Telephone Number:  301-474-1136 Mobile Telephone Number:  
>> 301-343-1457 FIRE SPRINKLERS SAVE LIVES - Can you live without them?
>> 
>> -----Original Message-----
>> From: [email protected] 
>> [mailto:[email protected]] On Behalf Of 
>> Aaron Peck
>> Sent: Tuesday, April 08, 2014 8:21 AM
>> To: [email protected]
>> Subject: System Check Valve
>> 
>> Hey group, this may be a dumb question but does a sprinkler system "need"
> a check valve?
>> 
>> I have a situation where there's several containerized housing side by
> side. Each container has it independent lead in and riser.
>> 
>> None of the risers have check valves, only a valve, flow switch and
> test/drain valve. I'm doing an inspection and I'm not sure IF check valves
> are necessary. I can't find anything in the code explicitly stating it needs
> one.
>> 
>> Since it's feed from one source, I'm checking for a main check valve/ back
> flow now, and since it's more of a horizontal multi-story building lol only
> 2 or 3 heads per floor. I don't think it's required.
>> 
>> And besides just acting as a valve to prevent water leaving the system
> piping, I can't remember any other reason.
>> 
>> Sent from my iPhone
>> Aaron M. Peck, SET Fire Protection
>> Skype +1(202)407-9079
>> Cambodia +855(0)78700407
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to