Well that answers the five W questions, and why it's not in the 1978 code.
Thanks Larry.


On Fri, Apr 11, 2014 at 6:13 AM, Larry Keeping <[email protected]> wrote:

> From The Technical Committee Report for the 1982 edition of NFPA 13:
>
>         13- P107 - (5-5.6 and Figure 5-5.6 (New):  Accept in Principle
>         SUBMITTER: Ron Cote', Factory Mutual Research Corp.
>         RECOMMENDATION:  Add a new section to read:
>         5-5.6  Small loading docks, covered platforms, ducts or similar
>         small unheated areas may be protected by dry pendent sprinklers
>         extending through the wall from wet sprinkler piping in an
>         adjacent heated area, as shown in Figure 5-5.6.
>
>         Where possible, the dry pendent sprinkler shall extend down at a
>         45° angle. The width of the area to be protected shall not
>         Exceed 7 1/2 ft (2.3 m). Sprinklers shall be spaced not over
>         12 ft (3.7 m) apart.
>             Add a new Figure 5-5.6
>         ...
>         SUBSTANTIATION:  The above proposed alternative provides a
>         workable solution where antifreeze systems are prohibited.
>
> Other than later being moved to the Appendix (Annex), it has remained
> virtually unchanged since that time.
>
> As I remember it, horizontal sidewall sprinklers had only been on the
> market for a few years prior to this and dry horizontal sprinklers did not
> become available until many years afterwards.
>
>
> Larry Keeping, P.Eng.
>
> Professional Loss Control
> 3413 Wolfedale Road, Suite 6
> Mississauga, Ontario
> L5C 1V8
>
> Phone:   905-949-2755, ext. 204
> Fax:        905-949-1752
>
> E-mail:    [email protected]
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Steve Leyton
> Sent: April-10-14 4:37 PM
> To: [email protected]
> Subject: Fig. A.8.15.7
>
> Anyone out there, committee members or clairvoyants, who can say why this
> illustration shows a dry-pendent sprinkler in what appears to be a
> non-conforming orientation?
>
> Thanks,
> SML
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to