Well, that's pretty much the final nail in that box lid.    Thank you Larry and 
everyone else for your input.

Steve

 




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Larry 
Keeping
Sent: Friday, April 11, 2014 6:14 AM
To: [email protected]
Subject: RE: Fig. A.8.15.7

>From The Technical Committee Report for the 1982 edition of NFPA 13:

        13- P107 - (5-5.6 and Figure 5-5.6 (New):  Accept in Principle
        SUBMITTER: Ron Cote', Factory Mutual Research Corp.
        RECOMMENDATION:  Add a new section to read:
        5-5.6  Small loading docks, covered platforms, ducts or similar
        small unheated areas may be protected by dry pendent sprinklers
        extending through the wall from wet sprinkler piping in an
        adjacent heated area, as shown in Figure 5-5.6.
        
        Where possible, the dry pendent sprinkler shall extend down at a 
        45° angle. The width of the area to be protected shall not
        Exceed 7 1/2 ft (2.3 m). Sprinklers shall be spaced not over
        12 ft (3.7 m) apart.
            Add a new Figure 5-5.6
        ...
        SUBSTANTIATION:  The above proposed alternative provides a 
        workable solution where antifreeze systems are prohibited.

Other than later being moved to the Appendix (Annex), it has remained virtually 
unchanged since that time.

As I remember it, horizontal sidewall sprinklers had only been on the market 
for a few years prior to this and dry horizontal sprinklers did not become 
available until many years afterwards.


Larry Keeping, P.Eng.

Professional Loss Control
3413 Wolfedale Road, Suite 6
Mississauga, Ontario
L5C 1V8

Phone:   905-949-2755, ext. 204
Fax:        905-949-1752

E-mail:    [email protected]

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve 
Leyton
Sent: April-10-14 4:37 PM
To: [email protected]
Subject: Fig. A.8.15.7

Anyone out there, committee members or clairvoyants, who can say why this 
illustration shows a dry-pendent sprinkler in what appears to be a
non-conforming orientation?     

Thanks,
SML
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to