And there's another point of discussion, how about that extrapolation at 20 psi.

What is the value of that number in reality?

I've seen 20 psi flow rates that we knew without any doubt were unachievable by 
the municipal water supply yet when trying to convince an owner that the water 
supply would not meet his system demand and the site would require a pump and 
tank, they would quickly point to the 20 psi flow rate and say "there, see 
we've got lots of water!"   It just confuses the uninformed.

I've also seen the additional data point of how much flow you get when at 0 
psi.  I'm still trying to get my head around that one.  Maybe someone can 
explain it.

So why put these fictional numbers on a test report?



Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mark A. Sornsin, P.E.
Sent: Wednesday, May 14, 2014 9:34 AM
To: [email protected]
Subject: RE: Can a hydrant flow from the pumper connection be used for the 
hydraulic calculations ?

Steve - you seem to be off on a tangent and did not understand the question. 
Its o.k. - that happens at your age.

I agree with Travis. I have done several water flow tests using the 4-1/2" 
port.  Apply the proper coefficients and life is good. Of course, flowing that 
port can have logistical problems due to the large amount of water and/or 
damage cause by the discharge - so be careful, plan accordingly, or find an 
alternative approach if necessary.

But he raises another peeve of mine. Further to Ron's comments, why do we have 
to reduce residual pressure to the point of being at least 25% lower than the 
static? If my sprinkler design anticipates 700 gpm for sprinklers and hose 
combines, and I run a flow test that produces 1,000 gpm with only a 1 psi drop 
in pressure, why would I attempt to open more ports or hydrants?

In this example we have a flat curve. We're going to need to flow a huge amount 
of water relative to my design demand to achieve the prescribed 25% drop. To 
what benefit would we do such a thing? The only reason I can imagine is 
"because our contract/AHJ says so" - which a crappy reason, but may be legit, 
sadly.

My personal belief is that 291 requires a certain drop in pressure because they 
want better accuracy for when they extrapolate to a residual pressure of 20 
psi.  I.e., the flow test is for fire departments to evaluate available 
firefighting water for their purposes - not necessarily for sprinkler design 
purposes.  Will this method give more accurate result for sprinkler design as 
well? Yes - but too often it is a level of accuracy not needed (as in my 
example above) and is not worth the effort expended.



Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack
Sent: Tuesday, May 13, 2014 4:12 PM
To: [email protected]
Subject: Re: Can a hydrant flow from the pumper connection be used for the 
hydraulic calculations ?

Are you asking if you can do a flow test from the pumper connection?  If so, 
then sure you can.  You just need to modify the coefficient based on your pitot.

How are you inflating the gpm?  If you measure 1200 gpm from the 2½" and you 
measure 2000 gpm from the 4.5", how is that inflating flow?  You should 
typically have a lower residual pressure when flowing the pumper connection 
than the 2½" connection.

If you are looking to 291 for direction, are you getting the required 25% drop 
in static and residual from your 2½" flow?  If not, what do you do?  You are 
required to open up additional hydrants to get the flow.
So, to get additional flow, you can also flow from the pumper connection.

Maybe I am misunderstanding your question.

Travis Mack, SET
MFP Design, LLC

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to