Now that I understand the intent of the topic ...

Ironically, this underscores something that's somewhat controversial and is a 
current topic in the NFPA 14 revision cycle, i.e. currency of flow tests and 
the use of flow models in lieu of open port flow testing.  If you're dealing 
with a water agency that has their system(s) modeled, or uses a third party to 
run flow models, it can be determined with a very high level of accuracy just 
how much flow (and at what velocity) a particular leg or main will produce.   
Craig's point about a single 8" not likely producing 4,000 gpm may be true, but 
two or three 8" legs of a municipal grid certainly can and that's where 
extrapolation of flow test results or the use of a model can help a fire 
official determine whether a particular water supply is capable of delivering 
the require fire flow to particular parcel.

BTW Mark Sornsin, I've already heard about this from others so if you want to 
make fun of me anymore the line forms over there.

SL

 




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Wednesday, May 14, 2014 7:41 AM
To: [email protected]; [email protected]
Subject: RE: Can a hydrant flow from the pumper connection be used for the 
hydraulic calculations ?

I understand the purpose of the 20 psi value.  I have seen 20 psi values that 
in no way would flow.  4000 gpm+ though an 8" water main, or a flow value not 
achievable by the municipal water supply.  My point is there is a danger in 
posting non-verified values in a flow report.  If you want to know what's 
available at 20 psi then flow the system until it bottoms out at 20 psi then 
you have factual data.  Otherwise when it's needed most that fictional 4000 gpm 
may only actually be half or less.  In the midst of a fire fight, is not the 
time to find out reality and extrapolation are not the same.  Now I realize 
that most project do not require large flow rates, so it's typically not a big 
deal.  In the industrial world, it's a big deal.  

We had a large project, water department did a flow test on a single hydrant 
butt with less than 1000 gpm flowing, extrapolated the curve out and modeled 
the water supply to the site which indicated we would have sufficient flow and 
pressures for our system.  When the final pump test was performed the flow rate 
was not there, not even close, the water department had assured the owner of a 
"robust" water supply. In actuality, they had "a lot of water" but their 
modeling was flawed and their test inconclusive due to extrapolation and not 
actual verification.  The owner had to add an above ground suction tank which 
delayed occupancy of the facility.   

Facts are facts and extrapolations are nothing but a good guess in many cases.  

Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to