Dewayne:

Why a reducing valve instead of a relief valve?    If the excess
pressure is at churn only, then a relief valve would be the ticket as it
only occurs in a no-flow condition.  This would mitigate Pete's concerns
about redundancy as prescribed in NFPA 14.

SML

 




-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Martinez, Dewayne
Sent: Tuesday, May 20, 2014 5:20 AM
To: [email protected]
Subject: Pressure reducing valve on fire pump

We have a situation where we have a pump that produces more than 175psi
at churn.  Can we put in a main pressure reducing valve after the pump
discharge to bring it all down to 175psi or do we need one for each
system?

Thanks,

Dewayne  

 