Once you are past the final control valve required by NFPA 20, that standard is 
no longer applicable (regarding use of a PRV - still not ok to use a relief 
valve).   As Pete already mentioned, it depends on what system the pump is 
feeding as to what arrangement is required for the PRV.  If it is a standpipe, 
then the redundant set-up identified in NFPA 14 is required.  NFPA 13 does not 
have a similar redundancy requirement so a single master PRV is allowed.

Roland
 
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org



On May 20, 2014, at 9:24 AM, Travis Mack <[email protected]> wrote:

> Doesn't it state in NFPA 20 that it is either bad design practice, or maybe 
> even prohibited to over size a pump and rely on a relief valve to take care 
> of the excess pressure.
> 
> I can see if you have a situation where the city water was upgraded and now 
> an existing pump is in this situation.  However, if new design, then 
> alternative options from the PRelV should be taken.
> 
> 4.7.7* Maximum Pressure for Centrifugal Pumps.
> 4.7.7.1 The net pump shutoff (churn) pressure plus the maximum static suction 
> pressure, adjusted for elevation, shall not exceed the pressure for which the 
> system components are rated.
> 4.7.7.2* Pressure relief valves and pressure regulating devices in the fire 
> pump installation shall not be used as a means to meet the requirements of 
> 4.7.7.1.
> 
> A.4.7.7 It is poor design practice to overdesign the fire pump and driver and 
> then count on the pressure relief valve to open and relieve the excess 
> pressure.Apressure relief valve is not an acceptable method of reducing 
> systempressure under normal operating conditions.
> 
> A.4.7.7.2 It is not the intent of this subsection to restrict the use of 
> pressure reducing valves downstream of the discharge isolation valve for the 
> purpose of meeting the requirements of 4.7.7.
> 
> I guess if you put it after the pump discharge control valve, then NFPA 20 no 
> longer applies and you go to NFPA 13 and/or 14 which may allow the device.
> 
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
> 
> On 5/20/2014 9:12 AM, Steve Leyton wrote:
>> Dewayne:
>> 
>> Why a reducing valve instead of a relief valve?    If the excess
>> pressure is at churn only, then a relief valve would be the ticket as it
>> only occurs in a no-flow condition.  This would mitigate Pete's concerns
>> about redundancy as prescribed in NFPA 14.
>> 
>> SML
>> 
>>  
>> 
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum
>> [mailto:[email protected]] On Behalf Of
>> Martinez, Dewayne
>> Sent: Tuesday, May 20, 2014 5:20 AM
>> To: [email protected]
>> Subject: Pressure reducing valve on fire pump
>> 
>> We have a situation where we have a pump that produces more than 175psi
>> at churn.  Can we put in a main pressure reducing valve after the pump
>> discharge to bring it all down to 175psi or do we need one for each
>> system?
>> 
>> Thanks,
>> 
>> Dewayne
>> 
>>  
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
>> .org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to