Good water or bad?

> On May 20, 2014, at 7:12 PM, "Cahill, Christopher" <[email protected]> 
> wrote:
> 
> I can't believe I'm asking this question after all these years.  Anyway, 
> swallowing pride and asking.
> 
> 2010 NFPA 13 strict Density/Area method 11.2.3.2 and 22.4.4.1.1.  Great big 
> room being subdivided. Existing system with a new wall added between heads on 
> a BL.  Contractor had to add a head on one side to preserve the existing 
> spacing (area) of the heads.  Without head over 130 sq.ft.  I take the 1.2 
> ^.5 of the area and get 46.5' required along the BL.  Original system lets 
> say calc'd 5 heads on the BL.  But now in the same 46.5' there are 6 heads on 
> the BL.  Do I ignore the wall and require a new calc?  What if the wall is 
> rated 1 hour do I ignore it?
> 
> I looked all over and can't seem to find anything definitive. Room design is 
> out so not a consideration.  22.4.4.1.1.1 simply says all the heads in the 
> 46.5'.  I can't find anything that says either to count the wall as a break 
> so measure 46.5' from the wall in each direction and still see if there are 5 
> head or ignore it and there are now 6 heads.  I find 11.1.2 that clarifies to 
> extend the density or not.  I don't think that's applicable exactly. The 
> question is not about whether to extend the density on either side. Let's 
> just say it's all OH.
> 
> It gets a little more complex as on the one side of the wall they cut a head 
> in on the BL but on the other side there is a perpendicular new wall and they 
> come off same BL and arm over to two more head so if I ignore the walls there 
> are now 8 heads off the 1 BL.
> 
> Prefer a code section or written reference 'cuz this is going to be a big 
> deal if we ignore the walls.  Ordinarily with unrated walls they are ignored 
> in density/area (of course can't find that reference).  I think I'm getting 
> tripped up with the rated portion? Or maybe I'm just tired????
> 
> Chris Cahill, PE*
> Associate Fire Protection Engineer
> Burns & McDonnell
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]<mailto:[email protected]>
> www.burnsmcd.com<http://www.burnsmcd.com/>
> *Registered in: MN
> 
> 
> Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For
> 
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to