Chris, I hope you meant for this to go to The Forum, not just me so I am trying 
my hand at re-directing it. 
Isn't it time we start seeing where semantics might be trying to over-ride 
physics?

> On May 20, 2014, at 7:44 PM, "Cahill, Christopher" <[email protected]> 
> wrote:
> 
> Trust me, my opinion is the same,  damn near any wall will stop the heat flow 
> long enough to get the right heads to operate.  This is strictly a code 
> question.  I'm OK and good at separating Code from opinion or even reality in 
> many cases.  Reality is wall will stop the heads on the other side for an 
> hour but Code seems to be silent.  OK when the unrated steel holding up wall 
> falls in 15 minutes assuming the sprinkler don't actually operate reality is 
> the 1 hour wall falls in 15 minutes. OK the valve is open, sprinklers operate 
> and the wall never fails until the municipal water supply runs out so all 
> this is moot in the real reality.  I sleep better following Code.
> 
> Chris 
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Brad Casterline
> Sent: Tuesday, May 20, 2014 7:33 PM
> To: [email protected]
> Subject: Re: Area/Density Method and Walls
> 
> The reason I ask Chris is, the calculation method sprung Not from "how fast 
> does an accidental fire get how hot", but "if we make the second piece inch 
> and a quarter can we reduce the main size a notch or two, and still get the 
> same water?" And I hear the first remote areas were round! I would consider 
> any barrier to the fire-driven heat flow, rated or not.
> 
>> On May 20, 2014, at 7:17 PM, Brad Casterline <[email protected]> wrote:
>> 
>> Good water or bad?
>> 
>>> On May 20, 2014, at 7:12 PM, "Cahill, Christopher" <[email protected]> 
>>> wrote:
>>> 
>>> I can't believe I'm asking this question after all these years.  Anyway, 
>>> swallowing pride and asking.
>>> 
>>> 2010 NFPA 13 strict Density/Area method 11.2.3.2 and 22.4.4.1.1.  Great big 
>>> room being subdivided. Existing system with a new wall added between heads 
>>> on a BL.  Contractor had to add a head on one side to preserve the existing 
>>> spacing (area) of the heads.  Without head over 130 sq.ft.  I take the 1.2 
>>> ^.5 of the area and get 46.5' required along the BL.  Original system lets 
>>> say calc'd 5 heads on the BL.  But now in the same 46.5' there are 6 heads 
>>> on the BL.  Do I ignore the wall and require a new calc?  What if the wall 
>>> is rated 1 hour do I ignore it?
>>> 
>>> I looked all over and can't seem to find anything definitive. Room design 
>>> is out so not a consideration.  22.4.4.1.1.1 simply says all the heads in 
>>> the 46.5'.  I can't find anything that says either to count the wall as a 
>>> break so measure 46.5' from the wall in each direction and still see if 
>>> there are 5 head or ignore it and there are now 6 heads.  I find 11.1.2 
>>> that clarifies to extend the density or not.  I don't think that's 
>>> applicable exactly. The question is not about whether to extend the density 
>>> on either side. Let's just say it's all OH.
>>> 
>>> It gets a little more complex as on the one side of the wall they cut a 
>>> head in on the BL but on the other side there is a perpendicular new wall 
>>> and they come off same BL and arm over to two more head so if I ignore the 
>>> walls there are now 8 heads off the 1 BL.
>>> 
>>> Prefer a code section or written reference 'cuz this is going to be a big 
>>> deal if we ignore the walls.  Ordinarily with unrated walls they are 
>>> ignored in density/area (of course can't find that reference).  I think I'm 
>>> getting tripped up with the rated portion? Or maybe I'm just tired????
>>> 
>>> Chris Cahill, PE*
>>> Associate Fire Protection Engineer
>>> Burns & McDonnell
>>> Phone:  952.656.3652
>>> Fax:  952.229.2923
>>> [email protected]<mailto:[email protected]>
>>> www.burnsmcd.com<http://www.burnsmcd.com/>
>>> *Registered in: MN
>>> 
>>> 
>>> Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For
>>> 
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to