For all practical purposes the air decompresses evenly throughout the
system so trip time will be essentially the same no matter where the device
is located as long as it's not on a line less than 2". So picture the
difference with air decompressing through a 2" hole and a 1/2" hole
anywhere. 15 open heads faster than 1 open head. The rub comes in with
transit time: as soon as water hits the exhauster it closes down so if the
exhauster is at the riser you get a fast trip but you still need to push
the remaining compressing air being displaced by the encroaching water out
the open heads. With the exhauster further down the line you still have the
extra 15"heads" open for a longer time. But since transit time once the DPV
valve has tripped is pretty quick this "extra" may be incidental. Maybe
someone should make an experiment. Oh, wait.... No more exhausters to
install so purely an academic endeavor. Probably could get a grant from
somewhere to study how they worked when we used them.


On Thu, May 22, 2014 at 7:17 AM, Roland Huggins
<[email protected]>wrote:

> But you have a shorter duration so it may be a wash.
>
>
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
>
>
>
>
>
> On May 22, 2014, at 6:05 AM, Jamie Seidl <[email protected]> wrote:
>
> > It may be difficult, but would it be possible to install a ITC manifold
> per
> > 2007 NFPA 13 7.2.3.6.1 (A7.2.3.7)?  Maybe that could help exhaust more
> air
> > out of the ITC and help with the transit time.
> > Jamie Seidl
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to