What I used to tell the distributors when I gave training seminars. The Star 
BB-Exhauster when used at the dry valve was just a big, ugly glorified 
accelerator, with a lot of maintenance issues. When used on the end of a feed 
main to helped the transit time by reducing the back pressure in the system to 
almost nothing. I was told by Fred Gloeckler the inventor, that the 
BB-Exhausters original intended use was at the ends of long skinny dry systems 
protecting piers and wharves in New York City.  They were tricky to set up in 
that they had to be adjusted so they would trip before the dry valve, if the 
dry valve tripped first they would probably never open.
 
Richard Mote ET
Designer
Rowe Sprinkler Systems, Inc.
PO Box 407
Middleburg, PA 17842
P- 877-324-ROWE
F- 570-937-6335
[email protected]
www.rowesprinkler.com



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of rongreenman .
Sent: Thursday, May 22, 2014 11:00 AM
To: [email protected]
Subject: Re: Exhausters

For all practical purposes the air decompresses evenly throughout the system so 
trip time will be essentially the same no matter where the device is located as 
long as it's not on a line less than 2". So picture the difference with air 
decompressing through a 2" hole and a 1/2" hole anywhere. 15 open heads faster 
than 1 open head. The rub comes in with transit time: as soon as water hits the 
exhauster it closes down so if the exhauster is at the riser you get a fast 
trip but you still need to push the remaining compressing air being displaced 
by the encroaching water out the open heads. With the exhauster further down 
the line you still have the extra 15"heads" open for a longer time. But since 
transit time once the DPV valve has tripped is pretty quick this "extra" may be 
incidental. Maybe someone should make an experiment. Oh, wait.... No more 
exhausters to install so purely an academic endeavor. Probably could get a 
grant from somewhere to study how they worked when we use
 d them.


On Thu, May 22, 2014 at 7:17 AM, Roland Huggins
<[email protected]>wrote:

> But you have a shorter duration so it may be a wash.
>
>
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
>
>
>
>
>
> On May 22, 2014, at 6:05 AM, Jamie Seidl <[email protected]> wrote:
>
> > It may be difficult, but would it be possible to install a ITC 
> > manifold
> per
> > 2007 NFPA 13 7.2.3.6.1 (A7.2.3.7)?  Maybe that could help exhaust 
> > more
> air
> > out of the ITC and help with the transit time.
> > Jamie Seidl
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958) _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to