It depends on how far away the flow test was taken, whether it is looped or 
gridded, and what the elevation changes are.  All of that needs to be 
considered and isn't by just calculating to the "point of connection".

Scott
 
(763) 425-1001x12 Office
(612) 759-5556 Cell

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tim Stone
Sent: Thursday, June 19, 2014 8:33 AM
To: [email protected]
Subject: RE: Location of Flow Test in Calc's

Brian,

I have always, if possible included the underground back to the flow test 
hydrants on tree style systems. Like yourself that was what I was taught.
If the underground is looped and several flow tests have been done on the loop, 
the tie in point should be fine too.


Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

                117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
                           [email protected]

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brian Harris
Sent: Thursday, June 19, 2014 9:19 AM
To: [email protected]
Subject: Location of Flow Test in Calc's

Was just told by one of our new designers that he was taught that it didn't 
matter where the flow test was taken on the underground that you just need to 
take it back to the tie in point at the main & that everywhere he's worked does 
it that way. News to me, any of you guys do it that way? If so how do you 
account for the loss in the underground to the test hydrant, elevation, etc.... 
?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to