Totally agree, however if the concept isn't understood it morphs to the email that started this thread. 400 gpm through old 4" or 6" is a bigger problem.
The right way is to calculate to the flow, get the information to do it right. If it is a single-feed loop and you are on the remote end of that loop from the supply and the test, you need to account for the loss. Scott (763) 425-1001x12 Office (612) 759-5556 Cell -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of IPA Sent: Thursday, June 19, 2014 9:08 AM To: [email protected] Subject: Re: Location of Flow Test in Calc's In light & ordinary hazards it's usually not a big deal as long as you've accounted for elevation differences. 400 gpm flowing through a thousand feet of 8" DIP equates to a little over 1 psi friction loss. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org