Totally agree, however if the concept isn't understood it morphs to the email 
that started this thread.  400 gpm through old 4" or 6" is a bigger problem.  

The right way is to calculate to the flow, get the information to do it right.  
If it is a single-feed loop and you are on the remote end of that loop from the 
supply and the test, you need to account for the loss.

Scott
 
(763) 425-1001x12 Office
(612) 759-5556 Cell

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of IPA
Sent: Thursday, June 19, 2014 9:08 AM
To: [email protected]
Subject: Re: Location of Flow Test in Calc's

In light & ordinary hazards it's usually not a big deal as long as you've 
accounted for elevation differences. 400 gpm flowing through a thousand feet of 
8" DIP equates to a little over 1 psi friction loss.