It would really depend on how close the test point was to the point of 
connection of the run-in to the main.  If the test point is 100 feet away and 
there's nothing between, then no biggie.

I take my calcs back through the UG main to the test point.  What does it hurt, 
be sure of your calcs and there's no question on accuracy. 

If the test point was back at a pump across the campus, his theory is blown.

I'm constantly amazed at the quality of shop drawings lately.  The field crews 
must do a lot of cussing at the designers based on some of the junk that's 
produced.

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Thursday, June 19, 2014 9:19 AM
To: [email protected]
Subject: Location of Flow Test in Calc's

Was just told by one of our new designers that he was taught that it didn't 
matter where the flow test was taken on the underground that you just need to 
take it back to the tie in point at the main & that everywhere he's worked does 
it that way. News to me, any of you guys do it that way? If so how do you 
account for the loss in the underground to the test hydrant, elevation, etc.... 
?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to