Haven't you guys beat this horse to death.........LOL

> From: [email protected]
> To: [email protected]
> Subject: RE: to Pitot or not to Pitot?
> Date: Fri, 20 Jun 2014 19:02:24 +0000
> 
> Here in Suffolk County New York we're required to adjust to a "historical 
> low". I've seen the water company drop the static as much as 25-30 psi... I 
> just finished a 10,000 sq.ft. gym with a 4"x3"x2" grid system feed from a 6" 
> supply due to the historical low... water company dropped my supply numbers 
> to 40/19 psi at 1975 gpm with 8.0 k heads for light hazard. Those number are 
> not sweet!! lol
> 
> I think we also have a couple of small water districts in Nassau county that 
> do the same... 
> 
> Steven MacKinnon
> Fire Protection Division
> Hartcorn Plumbing and Heating, Inc.
> 850 South Second Street
> Ronkonkoma, NY 11779
> Office 631-580-2300  Fax - 631-580-1090
> 
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Steve Leyton
> Sent: Friday, June 20, 2014 2:55 PM
> To: [email protected]
> Subject: RE: to Pitot or not to Pitot?
> 
> It may well be a requirement, but back to my rhetorical question: who's 
> actually doing it?
> 
> SL
> 
> 
> 
> 
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of Mark A. 
> Sornsin, P.E.
> Sent: Friday, June 20, 2014 11:39 AM
> To: [email protected]
> Subject: RE: to Pitot or not to Pitot?
> 
> Oh, and BTW, taking those seasonal/local/whatever fluctuations into account 
> IS noted in NFPA 13 - so one could argue correctly that it is a requirement 
> of "code" (assuming your code references NFPA 13).
> 
> Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer 
> | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
> http://www.kfiengineers.com
> 
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of Steve 
> Leyton
> Sent: Friday, June 20, 2014 12:57 PM
> To: [email protected]
> Subject: RE: to Pitot or not to Pitot?
> 
> 
> How many people, when requesting or performing a flow test or flow model, 
> specify that the values be measured at peak
> seasonal and peak day demands?   How much fluctuation does a given water
> system or zone experience in a day/week/month/year?  How many of us review 
> those fluctuations and factor them into a flow test once it's taken?
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com 
> ______________________________________________________________________
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
                                          
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to