I did a job in a beach community a while back and the fire marshal insisted 
that the water test be conducted between 2 and 3 PM on the 4th of July. I won't 
repeat what the water company told him.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)

> On Jun 20, 2014, at 2:55 PM, "Steve Leyton" <[email protected]> 
> wrote:
> 
> It may well be a requirement, but back to my rhetorical question: who's
> actually doing it?
> 
> SL
> 
> 
> 
> 
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of
> Mark A. Sornsin, P.E.
> Sent: Friday, June 20, 2014 11:39 AM
> To: [email protected]
> Subject: RE: to Pitot or not to Pitot?
> 
> Oh, and BTW, taking those seasonal/local/whatever fluctuations into
> account IS noted in NFPA 13 - so one could argue correctly that it is a
> requirement of "code" (assuming your code references NFPA 13).
> 
> Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
> Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
> http://www.kfiengineers.com
> 
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of
> Steve Leyton
> Sent: Friday, June 20, 2014 12:57 PM
> To: [email protected]
> Subject: RE: to Pitot or not to Pitot?
> 
> 
> How many people, when requesting or performing a flow test or flow
> model, specify that the values be measured at peak
> seasonal and peak day demands?   How much fluctuation does a given water
> system or zone experience in a day/week/month/year?  How many of us
> review those fluctuations and factor them into a flow test once it's
> taken?
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud
> service.
> For more information please visit http://www.symanteccloud.com
> ______________________________________________________________________
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to