Of course cooler only or 900sf
BUT
If he is an AHJ and he decides if you get a C of O, then he gets 1,500
sq ft.
Another "Authority Having Jurisdiction", but no common sense. What's new?
On 6/27/2014 1:11 PM, Bob wrote:
I have a 1,392 sf cooler. I calc'ed the entire area of the cooler and
submitted. The AHJ is telling me that I need to calc additional sprinklers
at the ceiling to have a 1500 sf design area. I don't think I need to do
this, I was looking at this as a separate fire area, and I don't see it
being much different than not adding heads below ducts or other large
obstructions. Do I need to calc additional sprinklers at the ceiling for
this application?