Of course cooler only or 900sf

                                        BUT

If he is an AHJ and he decides if you get a C of O, then he gets 1,500 sq ft.
Another "Authority Having Jurisdiction", but no common sense. What's new?



On 6/27/2014 1:11 PM, Bob wrote:
I have a 1,392 sf cooler.  I calc'ed the entire area of the cooler and
submitted.  The AHJ is telling me that I need to calc additional sprinklers
at the ceiling to have a 1500 sf design area.  I don't think I need to do
this, I was looking at this as a separate fire area, and I don't see it
being much different than not adding heads below ducts or other large
obstructions.  Do I need to calc additional sprinklers at the ceiling for
this application?

Thank You,

Bob Knight, CET III
208-318-3057
www.Firebyknight.com




--

West Tech Fire Protection, Inc.
11351 Pearl Road   / Strongsville, Ohio   44136
Phone 440 238-4800    Fax 440 238-4876