I agree to the extent this is how you decide to extend 15' past or not.  
Nowhere does it say you can be less than the remote area. You can do your 1,392 
OH and add 108 outside the cooler at whatever that density is required because 
the cooler wall is a physical barrier capable of delaying the heat....  You get 
1,500 total.  If the wall wasn't capable then you'd have to use the cooler 
density for the 108 extra (plus the 15' beyond).  That how I read it anyway 
it's a density section of code not an area section of code.    

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For





-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Bob
Sent: Friday, June 27, 2014 1:38 PM
To: [email protected]
Subject: RE: Cooler Calc

Chris,
NFPA 13 11.1.2 Adjacent Hazards or Design Methods. For buildings with two or 
more adjacent hazards or design methods, the following shall apply:
(1)  Where areas are not physically separated by a barrier or partition capable 
of delaying heat from a fire in one area from fusing sprinklers in the adjacent 
area, the required sprinkler protection for the more demanding design basis 
shall extend 15 ft (4.6 m) beyond its perimeter.

This simply says that there needs to be a portion or barrier capable of slowing 
heat release from one area to another.  

I'm not using room design, but area/density even in the instance of an area 
slightly less than 1500 ft2.


Thank You,

Bob Knight, CET III
208-318-3057
www.Firebyknight.com



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Cahill, Christopher
Sent: Friday, June 27, 2014 12:29 PM
To: [email protected]
Subject: RE: Cooler Calc

Except the cooler walls probably don't meet the definition for largest room 
because the wall aren't rated for OH (60 min right?).  You probably have an 
argument if the wall don't go to the structure then you are protecting under 
the obstruction so you are showing the most demanding above or below.  I'm 
assuming this is not its own system as well.  If it's its own system then you 
have an argument there as you never have to cross system boundaries. We once 
considered breaking up a small building into several under 1,500 sq.ft.
system to avoid a tank and pump.  We only considered never executed.   

Chris Cahill, PE*
Associate Fire Protection Engineer
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Bob
Sent: Friday, June 27, 2014 12:47 PM
To: [email protected]
Subject: RE: Cooler Calc

His stand is that I have one of three options that I have not used:
(1) Density/area curves of Figure 11.2.3.1.1 in accordance with the
density/area method of 11.2.3.2
(2) The room that creates the greatest demand in accordance with the room
design method of 11.2.3.3
(3) Special design areas in accordance with 11.2.3.4

Keep in mind that this is a jurisdiction that has told me in the past that
you can't use the exceptions in 13 (this was before they became part of the
body), and that they can't use common sense.



Thank You,

Bob Knight, CET III
208-318-3057
www.Firebyknight.com



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Tim Stone
Sent: Friday, June 27, 2014 11:41 AM
To: [email protected]
Subject: RE: Cooler Calc

The Cooler is a closed in room with a space above. You calculate all the
heads inside the cooler if less than 1500 SF. If the area outside the cooler
is fully sprinklered then you probably have performed calcs already. I'd ask
the AHJ to review NFPA 13.

Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

                117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
                           [email protected]

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Bob
Sent: Friday, June 27, 2014 1:12 PM
To: [email protected]
Subject: Cooler Calc

I have a 1,392 sf cooler.  I calc'ed the entire area of the cooler and
submitted.  The AHJ is telling me that I need to calc additional sprinklers
at the ceiling to have a 1500 sf design area.  I don't think I need to do
this, I was looking at this as a separate fire area, and I don't see it
being much different than not adding heads below ducts or other large
obstructions.  Do I need to calc additional sprinklers at the ceiling for
this application?

Thank You,

Bob Knight, CET III
208-318-3057
www.Firebyknight.com





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________