Except the cooler walls probably don't meet the definition for largest room because the wall aren't rated for OH (60 min right?). You probably have an argument if the wall don't go to the structure then you are protecting under the obstruction so you are showing the most demanding above or below. I'm assuming this is not its own system as well. If it's its own system then you have an argument there as you never have to cross system boundaries. We once considered breaking up a small building into several under 1,500 sq.ft. system to avoid a tank and pump. We only considered never executed.
Chris Cahill, PE* Associate Fire Protection Engineer Burns & McDonnell Phone: 952.656.3652 Fax: 952.229.2923 [email protected] www.burnsmcd.com *Registered in: MN Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Bob Sent: Friday, June 27, 2014 12:47 PM To: [email protected] Subject: RE: Cooler Calc His stand is that I have one of three options that I have not used: (1) Density/area curves of Figure 11.2.3.1.1 in accordance with the density/area method of 11.2.3.2 (2) The room that creates the greatest demand in accordance with the room design method of 11.2.3.3 (3) Special design areas in accordance with 11.2.3.4 Keep in mind that this is a jurisdiction that has told me in the past that you can't use the exceptions in 13 (this was before they became part of the body), and that they can't use common sense. Thank You, Bob Knight, CET III 208-318-3057 www.Firebyknight.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Tim Stone Sent: Friday, June 27, 2014 11:41 AM To: [email protected] Subject: RE: Cooler Calc The Cooler is a closed in room with a space above. You calculate all the heads inside the cooler if less than 1500 SF. If the area outside the cooler is fully sprinklered then you probably have performed calcs already. I'd ask the AHJ to review NFPA 13. Regards, G. Tim Stone G. Tim Stone Consulting, LLC NICET Level III Engineering Technician Fire Protection Sprinkler Design and Consulting Services 117 Old Stage Rd. - Essex Jct., VT. 05452 CELL: (802) 373-0638 TEL: (802) 434-2968 Fax: (802) 434-4343 [email protected] -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Bob Sent: Friday, June 27, 2014 1:12 PM To: [email protected] Subject: Cooler Calc I have a 1,392 sf cooler. I calc'ed the entire area of the cooler and submitted. The AHJ is telling me that I need to calc additional sprinklers at the ceiling to have a 1500 sf design area. I don't think I need to do this, I was looking at this as a separate fire area, and I don't see it being much different than not adding heads below ducts or other large obstructions. Do I need to calc additional sprinklers at the ceiling for this application? Thank You, Bob Knight, CET III 208-318-3057 www.Firebyknight.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org