I have a situation where I have a stepped obstruction against a wall. The 
occupancy is Light Hazard. The primary ceiling is 9'. There is a 4' wide soffit 
against a wall that is 1' lower. Under that soffit, there is one that is 1'-10" 
wide that sticks down an additional 1'. I presently have a sprinkler in the 
high area that is 3'-2" from the edge of the higher soffit. 

A sprinkler is going to be required under the under the first soffit because 
the sprinkler in the high area cannot protect underneath it based on section 
8.6.5.1.2(1) (NFPA 13 - 2002). However, the sprinkler in the high area can 
protect under the lower soffit per section 8.6.5.1.2(3). Can I install a 
sprinkler under the upper soffit and call it a day?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)