I think you are OK without the sprinkler in the lowest soffit.  But I'm not 
sure it's because of that section from the upper most head.  Perhaps from the 
lower head in the higher soffit. I always thought the section while saying 
protected really is/was an area that wouldn't get water there but was OK 
because it was small.  Look at the latest edition too.  I think you can get up 
to 4' wide now with soffits without heads under them in some circumstances and 
2' in other.

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Todd - Work
Sent: Monday, July 21, 2014 4:04 PM
To: [email protected]
Subject: stepped obstructions

I have a situation where I have a stepped obstruction against a wall. The 
occupancy is Light Hazard. The primary ceiling is 9'. There is a 4' wide soffit 
against a wall that is 1' lower. Under that soffit, there is one that is 1'-10" 
wide that sticks down an additional 1'. I presently have a sprinkler in the 
high area that is 3'-2" from the edge of the higher soffit. 

A sprinkler is going to be required under the under the first soffit because 
the sprinkler in the high area cannot protect underneath it based on section 
8.6.5.1.2(1) (NFPA 13 - 2002). However, the sprinkler in the high area can 
protect under the lower soffit per section 8.6.5.1.2(3). Can I install a 
sprinkler under the upper soffit and call it a day?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to