Cool. Another thing that you need to check is the architectural code
study. If the architect used the sprinkler allowance to increase the
square footage of the building, it is a 13 system regardless of how many
floors it is. I can't tell how many times I have seen this missed by the
architects and the sprinkler contractors.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
On 7/28/2014 9:35 AM, Brian Harris wrote:
Thanks guys, looks like I'll be getting a free lunch !!
Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On
Behalf Of Steve Leyton
Sent: Monday, July 28, 2014 12:00 PM
To: [email protected]
Subject: RE: 6 Story Hotel
Brian:
As I'm sure you know, the standard was titled for many years, "Installation of Sprinkler
Systems in Residential Occupancies up to and Including Four Stories in Height", but is
now titled, "... in Low-Rise
Residential Occupancies". (For whatever it's worth, I voted against
this as it's vague and not entirely aligned with existing definitions in
code(s) and standard(s). However, in the 2013, Section 1.1 it very
clearly states that the standard covers residential occupancies up to 60' (18
m) above grade plane (as defined in the applicable building code). The annex
material clarifies that this height is coincidental to the limit for Type V
construction, and so is aligned with the code in that regard and implies intent
to most closely manage Type V buildings,
which are almost always wood framed in R-group occupancies. So
literally and as written, if you have a 5- or 6-story building where the height
of the highest floor is 60' or less and it's of a construction type other than
Type V-A (which the code limits to 4 STORIES), then the answer to your question
(surprisingly) is yes, you can use 13R, taking it literally as it's written.
But keep in mind that this is all about what your locally adopted code allows,
and the code generally tells us when we can and can't use a
particular type of sprinkler system. You can't take a 13R for an extra
story except in R-2, and you can't take it in lieu of fire resistive
construction. And just because 13R leaves itself open to application in
buildings of Type III or II construction that may exceed four stories, your
code or building official may not. Also remember that if your code doesn't
reference the 2013 NFPA sprinkler standards, the older editions are still
implicitly limited to four stories.
The foregoing is my opinion only and does not necessarily represent the opinion
or intent of the NFPA 13D/13R Technical Committee on Residential Sprinkler
Systems. Not only that, this is a slippery slope so I also disclaim the email
chatter that's sure to follow, the second guessing and the uproar.
Steve Leyton
Protection Design & Consulting
San Diego, CA
-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of Brian
Harris
Sent: Monday, July 28, 2014 8:40 AM
To: [email protected]
Subject: 6 Story Hotel
Having a little debate here in the office..... Looking at a 6 story hotel and (1)
person wants to use NFPA-13R & (1) says you can't because it's over 4 stories
and you must use NFPA-13. Comments welcome .... :)
Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org