The note at the bottom of Table 508.4 states: S = Buildings equipped throughout with an automatic sprinkler system installed in accordance with Section 903.3.1.1.
903.3.1.1 NFPA 13 sprinkler systems. Where the provisions of this code require that a building or portion thereof be equipped throughout with an automatic sprinkler system in accordance with this section, sprinklers shall be installed throughout in accordance with NFPA 13 except as provided in Section 903.3.1.1.1. Note, it does not reference 903.3.1.2 which is for NFPA 13R sprinkler systems. Duane Johnson, PE Design Manager Strickland Fire Protection 5113 Berwyn Road College Park, Md. 20740 301-474-1136 Office 301-455-0010 Cell [email protected] -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Roland Huggins Sent: Friday, August 01, 2014 1:46 PM To: [email protected] Subject: Re: 6 Story Hotel IT has been awhile since I looked at this but I think you are reading that section out of context. I think there are 2 trade-offs including the reduction of the passive rating that is restricted to the presence of a full 13 system throughout BUT the IBC considers a building protected throughout even when a 13R system is installed. Awaiting input from our code boys and gals. Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Jul 28, 2014, at 12:37 PM, Steele, Andrew <[email protected]> wrote: > There are some other building code (and possibly even insurance risk > assessment) issues that are likely to arise when using a NFPA #13R system; a > 13R system IS NOT a fully protected building. For example, ICC Table 508 > "required separation of occupancies" does not recognize 13R systems, so if > the building has or gets multiple uses, it's a "non-sprinkled" building, > typically doubling the required separation . > > A. Steele _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org