The note at the bottom of Table 508.4 states: S = Buildings equipped throughout 
with an automatic sprinkler system installed in accordance with Section 
903.3.1.1.

903.3.1.1 NFPA 13 sprinkler systems. Where the provisions of this code require 
that a building or portion thereof be equipped throughout with an automatic 
sprinkler system in accordance with this section, sprinklers shall be installed 
throughout in accordance with NFPA 13 except as provided in Section 903.3.1.1.1.

Note, it does not reference 903.3.1.2 which is for NFPA 13R sprinkler systems.

Duane Johnson, PE
Design Manager
Strickland Fire Protection
5113 Berwyn Road
College Park, Md. 20740
301-474-1136 Office
301-455-0010 Cell
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Roland Huggins
Sent: Friday, August 01, 2014 1:46 PM
To: [email protected]
Subject: Re: 6 Story Hotel

IT has been awhile since I looked at this but I think you are reading that 
section out of context. I think there are 2 trade-offs including the reduction 
of the passive rating that is restricted to the presence of a full 13 system 
throughout BUT the IBC considers a building protected throughout even when a 
13R system is installed.

Awaiting input from our code boys and gals.

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Jul 28, 2014, at 12:37 PM, Steele, Andrew <[email protected]> 
wrote:

> There are some other building code (and possibly even insurance risk 
> assessment) issues that are likely to arise when using a NFPA #13R system; a 
> 13R system IS NOT a fully protected building.  For example, ICC Table 508 
> "required separation of occupancies" does not recognize 13R systems, so if 
> the building has or gets multiple uses, it's a "non-sprinkled" building, 
> typically doubling the required separation .
> 
> A. Steele

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to